[Equest-users] Percent of Hours Outside of Throttling Range

Seth P. Spangler sspangle at rmf.com
Fri Aug 21 11:11:06 PDT 2009


I personally use the SS-R report from the sim file. It breaks out which zones have unmet hours and whether or not they are under heated or cooled. It is also a good resource to check how your systems are operating as it includes hours in the part load ranges.

Seth Spangler, LEED® AP 
Project Engineer
 
RMF Engineering, Inc 
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641 
sspangle at rmf.com

-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Friday, August 21, 2009 1:26 PM
To: equest-users at lists.onebuilding.org; Imran Syed
Subject: Re: [Equest-users] Percent of Hours Outside of Throttling Range

Imran:

I believe you are correct. ASHRAE-90.1, Appendix G refers to actual number of hours.

However, if you also go the the Airside Tab in eQuest, then hit the Summary Tab below it, then click on the Project Icon in the tree diagram, you will get a zone by zone hours of Heating and Cooling loads not met. A really nifty scoreboard of data.

John Aulbach

--- On Fri, 8/21/09, Imran Syed <imran at hmsmep.com> wrote:

> From: Imran Syed <imran at hmsmep.com>
> Subject: [Equest-users] Percent of Hours Outside of Throttling Range
> To: equest-users at lists.onebuilding.org
> Date: Friday, August 21, 2009, 7:37 AM
> Users,
> In reference to the Pg 108 of 135 in the 3.63 Tutorial, it
> states "To
> calculate the total number of hours outside
> the throttlig range, multiply the percentage reported here
> by the "Hours
> Fans ON" reported on SS-E".
> 
> I am modeling a School and the percent of hours under
> throttle range is 12%.
> One of the comments from the LEED reviewer was that it
> would be 1050 hours
> (12% of 8760).
> The total number of hours the fans are working are 2000
> hours.
> Would it be right if I send a response back stating the
> Unmet hours are (12%
> of 2000 = 240 hours).
> Any comments will be greatly appreciated.
> 
> Thanks,
> Imran Syed, LEED AP
> HMS Engineering
> "Where air,water and fire behave"
> 
> Chicago Office
> 414 N. Orleans, St#306,
> Chicago, IL 60654
> Tel: 312-661-1516
> Fax: 312-661-1517
> email: imran at hmsmep.com
> 
> 
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank
> message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> 


      
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG



More information about the Equest-users mailing list