What this means is that you cannot exhaust more air than the outside air
supplied. To fix it - either reduce your exhaust or increase you outside
air cfm (which the program has automatically done for you). In cases
where you are exhausting more air than supplying (to negatively
pressurize), I am not sure eQUEST will allow for that (I could be wrong
here).  

 

Vikram Sami, LEED AP 
Direct Phone 404-253-1466 | Direct Fax 404-253-1366 

LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361 
Responsive Design * Technological Expertise * Exceptional Service 
Please visit our new website | www.lordaecksargent.com
<file:///\\www.lordaecksargent.com\> 

P Think GREEN before you print.

 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kevin
Felt
Sent: Thursday, February 19, 2009 12:20 PM
To: equest-users at lists.onebuilding.org
Subject: NINJA-SPAM:[Equest-users] Need help with Warnings and Errors

 

Hey All,

I have warnings and errors that I do not understand what they mean.
Also, how do I fix them?  My exhaust CFM is smaller than the outside air
CFM in most cases.

Thanks,

Kevin

 

**WARNING***************************************************************
*******

             el. plumb. teledata rooms        has EXHAUST-CFM greater
than ASSIGNED-CFM.

             ASSIGNED-CFM has been reset equal to EXHAUST-CFM.

 

 
**WARNING***************************************************************
*******

             ZONE Comm Rm (HP-5,ERV-1) zone        in SYSTEM PTAC
Community HP-5 ERV-1       

             has unused EXHAUST-CFM specified.

             This has been converted to outside air.

 

***ERROR****************************************************************
*******

             ZONE Elec,Trash,Main(B-1) zone        in SYSTEM Unit Htr
Elec,Trash,Maint       

             has unused EXHAUST-CFM specified.

             This has been converted to outside air.

 

**WARNING***************************************************************
*******

             ZONE Unit 410 (HP-1) zone             in SYSTEM PTAC 410
HP-1                   

             has unused EXHAUST-CFM specified.

             This has been converted to outside air.




****** FATAL DESIGN ERRORS IN SYSTEMS ******

 

 

 

Kevin A. Felt

Kevin  A. Felt

Senior Technical Analyst

QA Designee

MaGrann Associates

856-722-9799

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090219/8ffe03e3/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 125380 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090219/8ffe03e3/attachment-0002.png>


More information about the Equest-users mailing list