[Equest-users] Sizing of equipment
Carol Gardner
gems at spiritone.com
Tue Jan 13 08:41:48 PST 2009
Also, make sure the throttling range is 4-6 not whatever it defaults
too. There is a writeup in online help talking about why you should do so.
Carol
Sam Mason wrote:
>
> Janne,
>
> Without information on HW loop temp, cooling system type and control,
> and heating control, it’s tough to figure out what is going on with
> your model. That being said, I will provide what help I can. The
> sizing ratios on the coils only increase the coil size and do not
> increase airflow which is generally why zones will have hours out of
> range. Check the minimum flow ratio and airflow to your zones and make
> sure they are appropriate for the loads in the space. With regards to
> your system setup, make sure your reheat setpoints and supply air
> setpoints are consistent.
>
> For future reference, if you provide the input file, myself or others
> on the list serve will be able to better respond to future questions.
>
> Sam
>
> --
> Sam Mason
> Atelier Ten
> sam.mason at atelierten.com
>
> *From:* equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Kairento, Janne
> *Sent:* Tuesday, January 13, 2009 11:03 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Sizing of equipment
>
> Hey All,
>
> I am running a load with many zones on 5 floors totaling over 300
> zones. There are some zones with many unmet hours, some of the core,
> some perimeter. I went in and changed the sizing ratio of these zone
> to reduce the unmet heating hours. I am modeling this building with 9
> AHU’s, all VAV w/ reheat. Does anyone have any insight or suggestions
> on why or how these unmet hrs. exist. I have changed the hot water
> loop flow GPM but it had no effect on the unmet heating hrs. so I
> deduced this is not the cause.
>
> *Janne Kairento, E.I.T., LEED AP*
> */Cosentini Associates/*
> One Broadway
> Cambridge, MA 02142
> Phone: 617.494.9090
> Fax: 617.494.9292
>
> *Please consider the environment before printing this e-mail*
>
>
> NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if
> any) are intended solely for the use of the addressees hereof. In
> addition, this message and the attachments (if any) may contain
> information that is confidential, privileged and exempt from
> disclosure under applicable law. If you are not the intended recipient
> of this message, you are prohibited from reading, disclosing,
> reproducing, distributing, disseminating or otherwise using this
> transmission. Delivery of this message to any person other than the
> intended recipient is not intended to waive any right or privilege. If
> you have received this message in error, please promptly notify the
> sender by reply E-mail and immediately delete this message from your
> system.
> ________________________________________________________________________
> This e-mail has been scanned for all viruses by Star. The
> service is powered by MessageLabs. For more information on a proactive
> anti-virus service working around the clock, around the globe, visit:
> http://www.star.net.uk
> ________________________________________________________________________
>
> ______________________________________________________________________
> This email has been scanned by the MessageLabs Email Security System.
> For more information please visit http://www.messagelabs.com/email
> ______________________________________________________________________
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
> ------------------------------------------------------------------------
>
>
> No virus found in this incoming message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.176 / Virus Database: 270.10.6/1891 - Release Date: 1/13/2009 8:17 AM
>
>
More information about the Equest-users
mailing list