[Equest-users] Spam: MIN-AIR-SCH and -999
Brahme, Rohini UTRC
BrahmeR at utrc.utc.com
Mon Jan 19 10:08:52 PST 2009
Thanks. This worked. I had tried others - multiplier, on/off flag, which
don't work.
-Rohini
-----Original Message-----
From: Jay Keazer [mailto:JKeazer at tmecorp.com]
Sent: Monday, January 19, 2009 12:24 PM
To: Brahme, Rohini UTRC; Equest-users at lists.onebuilding.org
Subject: RE: Spam:[Equest-users] MIN-AIR-SCH and -999
I believe you have to use the schedule type "Frac/Design"
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brahme,
Rohini UTRC
Sent: Monday, January 19, 2009 10:23 AM
To: Equest-users at lists.onebuilding.org
Subject: Spam:[Equest-users] MIN-AIR-SCH and -999
There was a post some time back on how to incorporate -999 in the
Min-Air-Sch. Any resolution on that? The schedule type fraction does not
allow for -999, and the min-air-sch seems to take only sch of type
fraction as input. Following is the info from the help file
Thanks,
-Rohini
MIN-AIR-SCH
Takes the U-name of a SCHEDULE that contains hourly values of the ratio
of minimum outside air flow to supply air flow. Values in the
MIN-AIR-SCH vary from 0.0 (no outside air flow; economizer inactive if
specified) to 1.0 (100% outside air flow). A value of 0.001 actives the
economizer. A value of -999 returns the hourly value to MIN-OUTSIDE-AIR
or to the program's calculated minimum outside air value (found on
report SV-A for the SYSTEM or for each zone for zonal systems). During a
warmup period, this schedule is normally set to zero and can then be set
to -999 during other hours to allow the specified or calculated
ventilation minimum damper position to be used. Note that schedules are
ignored in the design routines; therefore, the minimum ventilation air
desired for design must be specified either at the zone or system level.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Equest-users
mailing list