[Equest-users] High boiler energy use compared to HW loop demand
Jeremy McClanathan
jmcclanathan at CDiengineers.com
Tue Jun 16 10:34:33 PDT 2009
I have had the same problem when I let EQUEST automatically size the boiler for me. In my situation, EQUEST drastically oversized the boiler so it was running at 10% capacity 90% of the time. You can check to see if you have the same problem by looking at report PS-C to see what part load range your boiler is operating at. To fix the problem, first I manually set the capacity of the boiler, which helped a lot, but the program was still over estimating the energy consumption. Then, I created a custom performance curve using actual data for my boiler. That solved my problem.
From: Josh Doherty [mailto:jdoherty at dcengineering.net]
Sent: Tuesday, June 16, 2009 10:14 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] High boiler energy use compared to HW loop demand
I have a situation where my boiler energy use (= 950 MBtu) is extremely high compared to the hot water loop demand = 550 MBtu. The modeled efficiency of the boiler is 80%...which should result in an estimated 690 MBtu of boiler energy use. Any ideas what could be going on here? Thanks.
Josh Doherty
This email message, including any attachments, is for the sole use of the intended recipient and may contain confidential, proprietary, and/or privileged information, as well as content subject to copyright and other intellectual laws. If you are not the intended recipient, you may not disclose, use, copy, or distribute the email message or its attachments. If you believe you have received this email message in error, please contact the sender by reply email, immediately delete this email and destroy copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090616/07d77fe5/attachment-0001.htm>
More information about the Equest-users
mailing list