[Equest-users] High boiler energy use compared to HW loop demand

B. Fountain bfountain at greensim.com
Tue Jun 16 10:43:17 PDT 2009


If you are manually setting the boiler capacities -- you may also wish to
set the heating loop sizing to primary from the default secondary where it
is sized based on the coils etc.

> I have had the same problem when I let EQUEST automatically size the
> boiler for me.  In my situation, EQUEST drastically oversized the boiler
> so it was running at 10% capacity 90% of the time.  You can check to see
> if you have the same problem by looking at report PS-C to see what part
> load range your boiler is operating at.  To fix the problem, first I
> manually set the capacity of the boiler, which helped a lot, but the
> program was still over estimating the energy consumption.  Then, I created
> a custom performance curve using actual data for my boiler.  That solved
> my problem.
>
> From: Josh Doherty [mailto:jdoherty at dcengineering.net]
> Sent: Tuesday, June 16, 2009 10:14 AM
> To: equest-users at lists.onebuilding.org
> Subject: [Equest-users] High boiler energy use compared to HW loop demand
>
> I have a situation where my boiler energy use (= 950 MBtu) is extremely
> high compared to the hot water loop demand = 550 MBtu.  The modeled
> efficiency of the boiler is 80%...which should result in an estimated 690
> MBtu of boiler energy use.  Any ideas what could be going on here?
> Thanks.
>
> Josh Doherty
>
>
>
>
> This email message, including any attachments, is for the sole use of the
> intended recipient and may contain confidential, proprietary, and/or
> privileged information, as well as content subject to copyright and other
> intellectual laws.  If you are not the intended recipient, you may not
> disclose, use, copy, or distribute the email message or its attachments.
> If you believe you have received this email message in error, please
> contact the sender by reply email, immediately delete this email and
> destroy copies.
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>





More information about the Equest-users mailing list