actually, you need to move the OA-FROM SYSTEM to be defined first in the inp
file. You should have one of these.
--
Karen
On Wed, Jun 17, 2009 at 9:28 AM, Kimberly Killian <
kimberly at northernarchitects.com> wrote:
> Good afternoon,
>
> I am trying to add a mixed air unit onto a four-pipe fan coil system
> through the use of a dummy zone, from which my real zones will get their
> outside air. I get the following error:
>
> "EL1 Sys1 (FC) (G.E16) defined before its OA-FROM-SYSTEM. This will cause
> incorrect OA temperature calculation. Move this SYSTEM to be defined before
> its OA-FROM-SYSTEM in the project BDL input file."
>
> The catch is that there is no BDL file, as the simulation aborts before it
> is complete. Is there another way to define the MAU before the Fan Coil
> System. I have searched a number of terms in the user's group and there are
> many questions related to this topic, but I can't find any answers. Any help
> would be appreciated.
>
> Regards,
> Kimberly Killian
> Northern Architects, Inc.
> 207 King Street Suite 3
> Burlington VT 05401
> T: 802-658-1953
> F: 802-658-2975
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090617/bfff19d8/attachment-0002.htm>
More information about the Equest-users
mailing list