Make sure the Billing unit thermal value is correct. It defaults to 1,000,000 Btus as the unit of measurement. If the utility rate is in Ton-days, say 3.50 per ton-day then you need to change that number to 288,000.
1 ton = 12,000 btuh
1 ton-day = 12,000 btuh * 24 hours = 288,000 btus
Timothy Howe, MS, LEED® AP
Mechanical Engineer
Stantec
2060 Brighton-Henrietta Town Line Road
Rochester NY 14623-2792
Ph: (585) 413-5347
Fx: (585) 272-1814
Cell: (585) 330-8681
stantec.com <http://www.stantec.com/>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Seth P. Spangler
Sent: Thursday, June 18, 2009 8:17 AM
To: wallie padero; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] District Cooling
Short answer YES!
In brief you will connect your building to a chilled water loop and put an energy meter on the loop to calculate the amount of energy used. You can then add an energy rate to the chilled water meter to calculate your annual cost.
However, if this is a LEED building registered in LEED NC v2.2 (and some other versions) after May 28th 2008 you MUST use the LEED document "Required Treatment of District Thermal Energy..." which will significantly change how your project will be modeled.
Seth Spangler, LEED® AP
Project Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641
sspangle at rmf.com
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of wallie padero
Sent: Thursday, June 18, 2009 2:36 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] District Cooling
Hi guys!
Can we model a project being served by a District Cooling Plant in E-quest?
More thanks in advance.
Wallie
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090618/f006c2ba/attachment-0002.htm>
More information about the Equest-users
mailing list