[Equest-users] Baseboard heaters
Bishop, Bill
bbishop at PathfinderEngineers.com
Fri Jun 26 07:48:27 PDT 2009
Rod,
Check the SS-R reports to determine your unmet load hours. If your unmet
heating hours are low or zero with the unit heaters alone, you are
probably overheating the space by the way you are modeling the
additional baseboards. For example, I have had trouble in the past when
selecting outdoor reset for the baseboard control, and use thermostatic
instead.
Regards,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rod A.
Crousey
Sent: Friday, June 26, 2009 10:17 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseboard heaters
I have a heating only space with forced ventilation unit heaters. I've
tried modeling this space with and without baseboard heaters. When I
add baseboard heaters with the unit heaters, my annual heating
consumption triples. I was not expecting this to have a drastic impact
on the natural gas usage. Does this mean that my model without the base
board heaters is not meeting all of the heating loads? I've checked the
equipment size against the peak demand and it seems adequate and the AHU
schedule does not indicate any hours outside the equipment capacity.
What is causing the apparent change in load between these two models?
-Rod