[Equest-users] Cooling Energy Consumption
Kevin Campbell
Kevin.Campbell at megroup.com
Tue Mar 24 08:27:24 PDT 2009
Sorry should have been more clear, it's a water cooled VAV system - single AHU for the building, the PS-A report lists Total Cooling as 1040 MBTU, the SS-A report lists Cooling Energy as 1019 MBTU, but the BEPS which should be the total if I'm not mistaken has a Space Cooling value of only 202 MBTU.
Thanks,
Kevin Campbell
Energy Modeler
M.E. Group, Inc.
Green Services Division
O: 800.200.9160 ext. 2129
C: 402.719.4228
engineering your environments
Click Here to Visit: www.MEGroup.com<http://www.megroup.com/>
P Do you really need to print this e-mail?
From: Mark Nieman [mailto:MARKN at McKinstry.com]
Sent: Tuesday, March 24, 2009 10:16 AM
To: Kevin Campbell; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Cooling Energy Consumption
The SS reports are system level only (think air handlers). The PS and PV reports are plant level (think chilled water plant). The BEPS report includes the entire energy associated with Cooling Energy, where the SS report may not (depending on your system). Check the PV-A, PS-A, PS-E, PS-C and PS-D reports to see if those make sense.
Mark Nieman, PE, CEM | McKinstry | Sr. Energy Engineer
d 206.832.8152 | m 206.510.4760 | f 206.832.8552
FOR THE LIFE OF YOUR BUILDING
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kevin Campbell
Sent: Tuesday, March 24, 2009 8:09 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Cooling Energy Consumption
My Space Cooling energy consumption from the BEPS report and the Cooling Energy on the SS-A report do not match, it seems to be leaving out a rather significant portion of the load. Why is this and is there a way to fix it?
Thanks,
Kevin Campbell
Energy Modeler
M.E. Group, Inc.
Green Services Division
O: 800.200.9160 ext. 2129
C: 402.719.4228
engineering your environments
Click Here to Visit: www.MEGroup.com<http://www.megroup.com/>
P Do you really need to print this e-mail?
________________________________
CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended only for the use of the individual or entity to whom or to which it is addressed and may contain information that is privileged, confidential, proprietary, and trade secret. If the reader of this message is not the intended recipient or an employee or agent responsible for delivering the message to the intended recipient, you are hereby notified that any dissemination, distribution, or reproduction of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately and discard the original message and any attachment(s).
This email is the property of McKinstry or one of its affiliates and may contain confidential and/or privileged information. If you are not the intended recipient or have received this e-mail in error please notify the sender immediately and delete this e-mail. Any unauthorized copying, disclosure or distribution of the material in this e-mail is strictly forbidden.
________________________________
CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended only for the use of the individual or entity to whom or to which it is addressed and may contain information that is privileged, confidential, proprietary, and trade secret. If the reader of this message is not the intended recipient or an employee or agent responsible for delivering the message to the intended recipient, you are hereby notified that any dissemination, distribution, or reproduction of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately and discard the original message and any attachment(s).
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090324/bf73743b/attachment-0001.htm>
More information about the Equest-users
mailing list