[Equest-users] eQuest - Modelling Elevators and Escalators
Cam Fitzgerald
cam at energyopportunities.com
Thu May 28 07:12:38 PDT 2009
Actually, with the methodology suggested below, the heat gain from the
equipment is not accounted for in the cooling energy consumption
calculations. This load should be added to the space in which the elevator
equipment is located since this is where the heat will be dissipated. In
the space properties box, click on the equipment tab and enter as equipment
load and select a default elevator schedule for the appropriate building
type. Other sources for elevator equipment schedules have been discussed
previously you may want to search the archives. We usually create an
elevator equipment electric sub-meter so we can verify the loads are
identical in both the baseline and Proposed models and easily isolate this
electric consumption for reporting this process load on the LEED Template.
Cam S. Fitzgerald, PE, LEED AP
Energy Opportunities, LLC
a 7group company
phone: (717) 292-2636 x11
fax: (717) 292-0585
e-mail: fitzgerald at sevengroup.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Howe,
Timothy
Sent: Thursday, May 28, 2009 7:48 AM
To: Aswan Ali; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest - Modelling Elevators and Escalators
Go to electric meter EM1 and click on tab Direct Loads and add the kW to the
interior direct loads and assign a schedule.
Timothy Howe, MS, LEED® AP
Mechanical Engineer
Stantec
2060 Brighton-Henrietta Town Line Road
Rochester NY 14623-2792
Ph: (585) 413-5347
Fx: (585) 272-1814
Cell: (585) 330-8681
<http://www.stantec.com/> stantec.com
The content of this email is the confidential property of Stantec and should
not be copied, modified, retransmitted, or used for any purpose except with
Stantec's written authorization. If you are not the intended recipient,
please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
_____
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Aswan Ali
Sent: Thursday, May 28, 2009 6:32 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest - Modelling Elevators and Escalators
Hi all,
Does anyone know how to model elevators and escalators on eQUEST for LEED?
Many thanks,
Aswan
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090528/fa7bfcfa/attachment-0002.htm>
More information about the Equest-users
mailing list