[Equest-users] R-Value problem
Eric O'Neill
elo at MichaelsEngineering.com
Fri Nov 6 13:08:07 PST 2009
All,
I don’t think air films or steel studs are going to account for a U-value of 20, but it’s hard to say what’s causing the problem without more information. We would probably need screenshots at a minimum, but the project .pd2 and .inp files would be the most helpful.
Eric
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Dakota Kelley
Sent: Friday, November 06, 2009 2:39 PM
To: Martin Ménard; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] R-Value problem
The conversion is accurate. If your calculated values don’t agree, it’s usually due to one or both of two things:
1) The conversion accounts for the inside air film (default of R-0.68), so you cannot simply take 1/R of the physical assembly to get the expected U-value
2) If you are specifying steel framed construction in the wizard, the insulation will be de-rated according to the stud depth and spacing. Refer to Table A9.2B in 90.1 for details.
Regards,
DAKOTA KELLEY
Project Designer
Office: 214-744-6199
Cell: 214-280-3825
Fax: 214-744-0770
http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis St. Suite 115
dakotak at teliospc.com <mailto:dakotak at teliospc.com> Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2009 Telios Corporation.
From: Martin Ménard [mailto:marmenard at gmail.com]
Sent: Friday, November 06, 2009 1:36 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] R-Value problem
Hi all eQUEST user!
I'm a bit confused about my input values inside the Wizard mode VS Detail mode.
In "Building Envelope Constructions" window (3 of 25) I put an Overall R-Value of 20 h-ft2-°F/Btu...
But, when I go into the spreadsheet view (in Detail mode) and take a look at the Constructions details, I see a U Value of 20 Btu/h-ft2-°F!?
It's not realy the same thing!
Did you know why the software does not make the convertion R to U value correctly? Or is it my mistake? Should I put a U value when the software asks me to put an R value in the Wizard window?
Thanks to all and sorry for my poor English (it's not my first language) ! :-)
Martin
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091106/05d04088/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091106/05d04088/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091106/05d04088/attachment-0002.jpeg>
More information about the Equest-users
mailing list