[Equest-users] Baseline Airflow Autosizing
Christina Galyfianaki
Christina.Galyfianaki at hurleypalmerflatt.com
Mon Oct 26 07:49:41 PDT 2009
Hello everybody
I use the auto-sizing option as Luca described and I trusted that the
when specifying the Sizing Ratio to be 1.15 for cooling and 1.25 for
heating would give me the equipment capacity as required by G3.1.2.2.
I then run the baseline for the first time just to get the supply
airflows (cfm) from the SV-A Report. Then I used this value to find the
fan Brake Horse power from Table G3.1.2.9 and then calculated the Pfan
from the formula G3.1.2.9
Then I find the fraction of fan power per flow Rate in kW/cfm and input
this value with a DT of 19.8 (as per G3.1.2.8)
It seemed to work fine and the USGBC accepted the model. I am really
interested to double-check with other modellers methodology.
But mostly I want to ask the following Question:
Do you use the auto-sizing method for the Proposed building?
You can still input the actual Sizing ratio, DT and kW/cfm of your
design that will determine your energy consumption and thus reflect your
design principles. I will appreciate the feedback of the experienced
users.
Kind Regards,
Christina
Christina Galyfianaki
Simulation Consultant
Building Physics Division
LCEA CIBSE Accredited, EPCs levels 3/4/5
hurleypalmerflatt
building sustainability
d: +44(0) 20 7535 3106
t: +44(0) 20 7535 3100
f: +44(0) 20 7535 3101
e: christina.galyfianaki at hurleypalmerflatt.com
w: www.hurleypalmerflatt.com <http://www.hurleypalmerflatt.com>
View company email disclaimer at:
http://owa.hurleypalmerflatt.com/disclaimer.asp
*
P Please consider the environment before printing this email.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Matutinovic, Luka
Sent: 26 October 2009 13:33
To: reniel barroso; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline Airflow Autosizing
Reniel,
Are you referring to the sizing runs from G3.1.2.2.1? If so, leave the
design cfm on each air-handler blank (see screenshot below) and eQuest
will size the flows based on the sizing option you've specified (Click
on a system, go the Basics tab, and see "Sizing Option").
If you need to size the baseline equipment capacity as per G3.1.2.2,
then multiply the auto-sized flows from the first step, by 1.25 for
heating and 1.15 for cooling and enter the result as the design cfm.
I think you might be able to do the second step directly by specifying a
sizing ratio (see second screenshot), although for whatever reason I
haven't done it this way in the past, so I'd be curious to hear from the
more experience eQuesters what approach they take.
Hope the helps,
Luka Matutinovic, B.A.Sc., LEED(r) AP
Green Building Consultant
T. 416.644.0649
F. 416.487.9766
Toll Free 1.888.425.7255
www.halsall.com
HALSALL ASSOCIATES LTD.
Toronto Richmond Hill Ottawa Sudbury
Burlington Calgary Vancouver Dubai
'50 Best Workplaces in Canada'
2009 Globe and Mail
P Please consider the environment before printing this e-mail
________________________________
From: reniel barroso [mailto:renielbarroso at yahoo.com]
Sent: Sunday, October 25, 2009 1:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Airflow Autosizing
I've been trying to look on the equest interface where we can set the
airflow to autosize itself as per LEED baseline requirement.
I don't think we have this option here. Have we?
Thanks in advance.
Reniel
________________________________
New Email names for you!
<http://sg.rd.yahoo.com/aa/mail/domainchoice/mail/signature/*http:/mail.
promotions.yahoo.com/newdomains/aa/>
Get the Email name you've always wanted on the new @ymail and
@rocketmail.
Hurry before someone else does!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091026/b03be46b/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 62767 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091026/b03be46b/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 5166 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091026/b03be46b/attachment-0005.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 86545 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091026/b03be46b/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 106222 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091026/b03be46b/attachment-0007.jpeg>
More information about the Equest-users
mailing list