[Equest-users] Error question
Brett Fero
bfero at robsonwoese.com
Mon Sep 14 12:21:52 PDT 2009
Lars,
My suggestion would be to open the bdl file and search for "error". This will indicated direct you to where error occurred. Too many errors and eQuest gives up.
If you are manually editing the inp file, make sure you have two periods ".." at the end of you commands as required.
Brett Fero, P.E., LEED AP
RobsonWoese Inc.
bfero at robsonwoese.com<mailto:bfero at robsonwoese.com>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Lars Fetzek
Sent: Monday, September 14, 2009 3:08 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Error question
eQuesters,
I included the following text in my .inp file, copied-and-pasted from an .inp file that eQuest generated. My intention is to edit it to reflect the conditions of the present project, which I really really don't want to have to re-create in the wizard, since I've already composed about 3,000 lines of .inp code for complex geometry, schedules, etc. As of yet, the only thing that I've edited are the U-names referring to the fan schedule, the heat schedule, the cool schedule, and the space - so that they match the present project. Scrolling down in this e-mail, you'll see the lovely error messages that appear when I load the .inp file into eQuest. Can anyone tell me what is wrong and how to fix it? (Yes, I clicked on the errors, but eQuest tells me nothing helpful.)
By the way, my concern here is only with HVAC errors and not with the electric meter error, which simply results from me having commented-out the electric meter code in the .inp file.
Thanks if you have advice...
Lars Fetzek, EI
Phoenix Engineering Group
Tampa, Florida
$ *********************************************************
$ ** **
$ ** HVAC Systems / Zones **
$ ** **
$ *********************************************************
"HVAC1 System" = SYSTEM
TYPE = PVAVS
HEAT-SOURCE = NONE
ZONE-HEAT-SOURCE = ELECTRIC
BASEBOARD-SOURCE = NONE
SIZING-RATIO = 1.15
MAX-SUPPLY-T = 95
MIN-SUPPLY-T = 55
ECONO-LIMIT-T = 65
ECONO-LOCKOUT = YES
OA-CONTROL = FIXED
FAN-SCHEDULE = "HVAC1 Fan Sch"
FAN-CONTROL = FAN-EIR-FPLR
SUPPLY-STATIC = 3.569
SUPPLY-EFF = 0.521452
RETURN-EFF = 0.53
FAN-EIR-FPLR = "Variable Speed Drive FPLR"
REHEAT-DELTA-T = 15
COOLING-CAPACITY = 379900
COOLING-EIR = 0.324232
CRANKCASE-HEAT = 0
FURNACE-HIR = 1.24067
..
"Zone Space 1A" = ZONE
TYPE = CONDITIONED
MIN-FLOW-RATIO = 0.3
FLOW/AREA = 0.5
OA-FLOW/PER = 155.325
EXHAUST-FLOW = 1130
EXHAUST-STATIC = 0.75
EXHAUST-EFF = 0.411758
DESIGN-HEAT-T = 68
HEAT-TEMP-SCH = "HVAC1 Heat Sch"
DESIGN-COOL-T = 76
COOL-TEMP-SCH = "HVAC1 Cool Sch"
SIZING-OPTION = ADJUST-LOADS
SPACE = "Space 1A Space"
..
[cid:image001.jpg at 01CA354F.13E4A300]
________________________________________________________________________
This Email has been scanned for all viruses by PAETEC Email Scanning Services, utilizing MessageLabs proprietary SkyScan infrastructure. For more information on a proactive anti-virus service working around the clock, around the globe, visit http://www.paetec.com.
________________________________________________________________________
________________________________
"This message is for the designated recipient only and may contain privileged, proprietary, or otherwise private information. If you are not the intended recipient, you are hereby notified that any disclosure, copying, distribution, or the taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please notify the sender immediately by e-mail and delete the original message."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/aac01564/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 161273 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/aac01564/attachment-0001.jpg>
More information about the Equest-users
mailing list