The delta T G.3.1.2.8 is referring to a 20 degree delta between room
cooling setpoint and supply air temperature.  For example:



Room Cooling Setpoint =        75 °F

20 °F delta from G.3.1.2.8  = -20 °F

Supply Air Temperature =      55 °F



A 20 degree fan delta T would be a MONSTER of a fan..



Robby Oylear, LEED® AP

Mechanical Engineer

direct: 206.788.4571

cell: 206.354.2721

www. <http://www.rushingco.com/> rushingco.com



From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chan,
Walter
Sent: Thursday, September 17, 2009 2:50 PM
To: Equest-users at lists.onebuilding.org
Subject: [Equest-users] G.3.1.2.8 Design Air Flow



When I use delta T 20F for supply fan, the CFM stays the same and the
cooling load is up 60% and heating load is slightly lower.  Any clue?



Is there a correct way to put in the Delta T 20F (after I set default and
not using fan static pressure) and eQuest will calculate the correct CFM?



Thanks for the help.