[Equest-users] G.3.1.2.8 Design Air Flow
Vikram Sami
VSami at lasarchitect.com
Thu Sep 17 15:09:00 PDT 2009
To follow up on what Robb said, the fan delta T is the heat gain across the fan from the fan motor.
You input your supply air temperature in this window:
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Robby Oylear
Sent: Thursday, September 17, 2009 5:53 PM
To: 'Chan, Walter'; Equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] G.3.1.2.8 Design Air Flow
The delta T G.3.1.2.8 is referring to a 20 degree delta between room cooling setpoint and supply air temperature. For example:
Room Cooling Setpoint = 75 °F
20 °F delta from G.3.1.2.8 = -20 °F
Supply Air Temperature = 55 °F
A 20 degree fan delta T would be a MONSTER of a fan..
Robby Oylear, LEED® AP
Mechanical Engineer
direct: 206.788.4571
cell: 206.354.2721
www.rushingco.com <http://www.rushingco.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chan, Walter
Sent: Thursday, September 17, 2009 2:50 PM
To: Equest-users at lists.onebuilding.org
Subject: [Equest-users] G.3.1.2.8 Design Air Flow
When I use delta T 20F for supply fan, the CFM stays the same and the cooling load is up 60% and heating load is slightly lower. Any clue?
Is there a correct way to put in the Delta T 20F (after I set default and not using fan static pressure) and eQuest will calculate the correct CFM?
Thanks for the help.
Walter W. Chan, P.E., LEED AP
CAS Group
1341 North Delaware Ave., Suite 500 | Philadelphia, PA 19125
T: 215.427.8711 | F: 215.427.8710
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090917/96252b8b/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 24103 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090917/96252b8b/attachment-0001.png>
More information about the Equest-users
mailing list