[Equest-users] Solar Gain Factor & Variable Infil Values
Nick Caton
ncaton at smithboucher.com
Tue Apr 20 15:26:36 PDT 2010
Piyush, I am but a humble user and not a developer or "expert," but I
can offer some fast suggestions - someone else may care to elaborate:
1. The solar heat gain factor (SHGF) used depends on the window
selected. Suggest checking out the DOE2 Glass Library if you haven't
already. Right-click nearly any input field, select "Tutorials and
Reference" from the context menu, and select the DOE2 Glass Library
excel spreadsheet.
2. If you asking whether the variability of solar heat gain (that
is, transmitted + absorbed radiation that flows inward) through a window
is accounted for, then the answer is yes. That varies hourly based on
the changes of incident sunlight, as affected by the fixed window
orientation, any building shades and/or other self-shading elements. If
instead you mean a variable shading coefficient (SC), as with automated
blinds and such, then the answer is also yes - via creating a custom
shading schedule.
3. Variable infiltration and ventilation rates are both model-able
in eQuest, and are two distinct topics...
a. For infiltration, suggest entering the detailed mode, opening
the properties for any space under "internal loads" tab, and exploring
the various infiltration methods that may be employed under the
infiltration tab, along with the corresponding help/dictionary entries.
The ACH rate method for example accounts for the hourly wind speed data
present in your weather file to determine the hourly ventilation rate.
b. For ventilation, you may observe "constant" ventilation rates,
but only if you chose to model as such. Be sure any and all methods of
varying the ventilation air rate are accounted for in your model.
Best of luck!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Piyush
Varma
Sent: Tuesday, April 20, 2010 3:40 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Solar Gain Factor & Variable Infil Values
Hi,
am a eQuest newbie, am doing some research wherein i need to know the
solar gain factor the windows use, also does eQuest take into account
Alternating Solar Gain Factor???I would also like to find out whether
variable infiltration flow rates (or variable ventilation values) are
taken into account??? the hourly report block i generated only gave me
same value for infiltration flow rates for all 24 hrs & for all 365
days.
Please help, this is regarding my Major Project at College & deadlines
are approaching.
Thanks in advance,
Regards,
Piyush Varma
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100420/67e67aeb/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100420/67e67aeb/attachment-0001.jpeg>
More information about the Equest-users
mailing list