[Equest-users] Toilet and Parking Exhaust
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Tue Aug 3 05:46:36 PDT 2010
Omar,
For parking deck fans, I have used a direct load on my meters.
I am not sure that the ASHRAE fan allowances were intended to account for fans that do not serve enclosed spaces. Therefore, I've used the same peak power in my baseline and proposed models.
The key variable is the schedule. ASHRAE 90.1-07 User Manual recommends using a schedule "based on likely use."
When installing controls that are not code-required (eg CO monitoring), I would argue that there should be fan power reductions over scheduled on/off and over full out use.
I believe this has been addressed in past posts to the list; I think the recommendation was to use "likely statistical schedules" of use, though I don't recall what these actually were?
The main trouble, in my mind, is I'm not sure we can argue that 100% on all the time control is a reasonable "baseline" for parking garage fans.
Disclosure: To date, I haven't submitted this approach to the GBCI reviewers.
Aaron Dahlstrom , PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 215-735-7290
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.akfgroup.com<http://www.akfgroup.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar Katanani
Sent: Thursday, July 29, 2010 12:00 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Toilet and Parking Exhaust
Dear all,
I was wondering what is the best way to model exhaust fans in the school toilets. I read some of the forum emails and what I'm doing now is that I select the space type of the bathroom to be "plenum". Then go to "Outdoor Air" tab and specify the flow in the exhaust "Flow" input box, then specify the kW/CFM. I did so but didn't notice a change in the ventilation fans consumption or in any other consumption.
1) Can someone show me how I can see this? I have like 10 toilets or so, and their effect can't be that negligible!
I have an underground parking with a supply fan and an exhaust fan (but no heating or cooling). I obviously couldn't specify the zone type to "Plenum" because then I won't be able to edit the supply rate. I put the zone type to "Conditioned", and specified the maximum cooling/heating rates of the parking to be 0 Btu/hr. I had an increase in the ventilation fans consumption (due to the 30,000CFM of supply/exhaust in the parking).
The problem is that I had a huge amount of additional cooling consumption! I do not want to cool the air in the parking.
2) What should I modify in order to have only ventilation in the parking without cooling?
I attach the files in this email, in case someone wishes to check them!
PS: for the Unmet hours problem I had before, I was able to solve it by looking into the Quality Control Report, then checking which zones had excessive under-cooling. I increased the air supply flow rate for these zones, and the problem is all fixed :D
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel: +961 (0) 1 971 255
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0)207 939 0989
Fax: +44 (0)207 939 0981
Website: www.ecoconsulting.net
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100803/6a24501d/attachment.htm>
More information about the Equest-users
mailing list