[Equest-users] assigning multiple HVAC systems to a zone
John Aulbach
jra_sac at yahoo.com
Wed Aug 11 12:11:44 PDT 2010
Ben:
Bottom line - you cannot have two systems in one zone.
You CAN, however, have baseboard heaters within a space on many systems. That
would be your finned tube radiators.
I believe you can do this within the Wizard.
John R. Aulbach, PE, CEM
Senior Energy Engineer
________________________________
PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com
________________________________
From: Ben Pressman <bpressman at practicalenergy.net>
To: equest-users at lists.onebuilding.org
Sent: Wed, August 11, 2010 11:59:41 AM
Subject: [Equest-users] assigning multiple HVAC systems to a zone
I have a building that has two distinct heating/cooling systems for a given
zone. There is a large multizone system with forced air blown over cold/hot
water coils that serves the entire building. Then there are finned radiators in
each room heated by hot water. How do I assign both systems to a given zone? The
wizard doesn't seem to allow this, and I haven't gotten too deep into detailed
mode yet with this model. Any help would be appreciated.
Thanks,
Ben
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100811/c5492a3a/attachment-0002.htm>
More information about the Equest-users
mailing list