[Equest-users] what HVAC system type for a building with residential and nonresidential?
zhiren zhou
zhouzr at cabr-sh.com
Tue Dec 14 18:18:05 PST 2010
Dear all:
My project is a 84- floor super-high building with 27 floors for
office and 47 floors for residential(hotel and apartment) and others for
retail and equipment floors. When I select baseline HVAC system Im confused
as both the two option below sounds rational:
1) The Note under TABLE G3.1.1A- Baseline HVAC System Types in Page
181 of ASHRAE 90.1 tells that : Where attributes make a building eligible
for more than one baseline system type, use the predominant condition to
determine the system type for the entire building.
2) The explanation in Page G-23 of ASHRAE 90.1 MANUAL tells that : If
a building has both residential and nonresidential spaces with their total
conditioned floor area both greater than 20,000 ft², for instance a
residential tower with retail and restaurants at the base, then the HVAC
system type is determined separately for the residential and nonresidential
portions.
So if I follow option 1 I should select PTAC for the whole building which I
think unsuitable. else if I follow option 2 I should select PTAC for
residential and VAV for office and others.
Which option should I follow?
Could anyone tell me? Thanks
Zhiren ZHOU