[Equest-users] windows on plenum walls
Karen Walkerman
kwalkerman at gmail.com
Thu Dec 2 08:08:50 PST 2010
I have found that this has to do with the system type you choose. If you
have a central system such as VAV reheat, which serves many zones, you'll
get one plenum. If you have PTACs, with one piece of equipment for each
zone, you'll have multiple plenums.
--
Karen
On Thu, Dec 2, 2010 at 11:03 AM, Pasha Korber-Gonzalez <
pasha.pkconsulting at gmail.com> wrote:
> So, I figured out where my plenum windows were going...Because eQuest set
> up a single plenum for my entire floor plan, as opposed to multilple plenum
> spaces for each Zoned space that I have.
>
> My new question that I haven't been able to figure out is this:
>
> When (or how to determine when) eQuest will create a single plenum for the
> entire floor plan, and when does it create a single plenum space for each
> space zoned in my floor plan?
>
> Sometimes I'll set up a model and it will do one approach and then
> sometimes I'll set up a model and it will create a single space plenum??
>
> Any hints anyone can give me are appreciated.
>
> thanks,
> Pasha
>
> On Wed, Dec 1, 2010 at 3:35 PM, Pasha Korber-Gonzalez <
> pasha.pkconsulting at gmail.com> wrote:
>
>> Hi All,
>>
>> I've always been able to do this before, but its not letting me do it
>> today on a model I am working on...
>>
>> I'm am trying to place some windows on the plenum walls. In real life
>> these are actually a spandrel panel. I'm in the custom window placement and
>> when I place the window on the plenum wall it shows up in the custom window
>> screen, but when I go to check my 3D view, the window on the plenum wall is
>> not displayed.
>>
>> Has anyone had this problem before? I've always been able to place
>> windows there before (I specifically remember being able to do it in the
>> window wizard for 3.63b version. I know I can verify thier existance when
>> I move to DDedit, but I'm just trying to be more efficient using my wizard
>> tools first.
>>
>> thanks,
>> pkg
>>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101202/9abd1867/attachment-0002.htm>
More information about the Equest-users
mailing list