[Equest-users] Reducing unmet hours
Haddad, Kamel
Kamel.Haddad at NRCan-RNCan.gc.ca
Wed Feb 17 06:50:06 PST 2010
Try setting the Thermostat Type for the zone to "REVERSE-ACTION" so that
your reheat comes on.
Kamel Haddad.
Building Energy Simulation
CanmetENERGY
Ottawa Ontario K1A0E4
Phone: 613-947-9822
Fax: 613-996-9909
Email: khaddad at nrcan.gc.ca
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Tomlinson, Scott
Sent: February 17, 2010 09:30
To: Tomlinson, Scott; equest-users at lists.onebuilding.org
Subject: [Equest-users] Reducing unmet hours
Hello eQuesters,
I am having a lot of trouble getting my unmet heating hours down. The
only system I can get to work is the multi-zone packaged system, but
this system has some simultaneous heating and cooling, and isn't the
best match for us. For some reason when I use the packaged variable
volume system (which is the best match for us) my unmet heating hours go
absolutely crazy. It's almost like the program isn't recognizing the
zone reheat, so areas aren't getting heated properly. Has anyone had a
similar issue? I attached my building model, if someone would be
willing to take a look it's AHU-1 and AHU-2 that we are having issues
with.
Thanks,
- Scott
__________________________________________
Scott Tomlinson, PE, LEED-AP
Mechanical
Symmes Maini & McKee Associates, Inc.
1000 Massachusetts Avenue, Cambridge, MA 02138
t: 617.520.9438
f: 617.354.5758
stomlinson at smma.com
www.smma.com <http://www.smma.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100217/c7af192f/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14792 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100217/c7af192f/attachment-0002.jpeg>
More information about the Equest-users
mailing list