[Equest-users] Baseline Modeling as per LEED district coolingrequirements
Sam Mason
sam.mason at atelierten.com
Wed Jul 7 06:49:51 PDT 2010
Mohammad,
You will keep the same the same system from step 1 to step 2 - fan coils with hot water boiler - per Table 3 in the DES guidelines. In step 2, you will create a minimally compliant cooling plant based on Appendix G modeling parameters and attach the fan coils to the plant.
Sam
--
Sam Mason
Atelier Ten
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mohammad Almasri
Sent: Wednesday, July 07, 2010 8:38 AM
To: eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED district coolingrequirements
Hi all,
I Am working now on a Residential tower supplied by a district cooling plant . The proposed design completed as per the LEED required treatment of district cooling . and two model performed (one with virtual chillers and the other one with chilled water meter to reflect the chilled water cost).
The problem that I have now is in the baseline.
In step one (modeled as cost neutral), the document say that the system will be based on table 3 instead of ASHRAE appendix G , system 2 (FCU will be use instead of PTHP).
Now for step two , what the system will be ; it should be a PTHP or a FCU with a chillers ?
Please I need your advice .
Best regards,
Mohammad Al-Masri
Simulation Engineer
CAPM,LEED AP BD+C
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The service is powered by MessageLabs. For more information on a proactive anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email ______________________________________________________________________
More information about the Equest-users
mailing list