[Equest-users] Baseline Modeling as per LEED districtcoolingrequirements

Cam Fitzgerald cam at energyopportunities.com
Thu Jul 8 09:11:05 PDT 2010


All:

I hate to disagree with Sam's response, but on page 6 of the USGBC DES document the description of the Model for Step 2 states, "The proposed case modeling requirements differ from those in ASHRAE 90.1-2004 Appendix G; however, the baseline case is modeled as instructed in Appendix G."  So for step 2 the baseline HVAC systems for the residential spaces would be PTHP, not AHU's as required for step 1.

Hope this helps!

Cam S. Fitzgerald, PE, LEED AP
 
Energy Opportunities, LLC
a 7group company

 -----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sam Mason
Sent: Wednesday, July 07, 2010 9:50 AM
To: Mohammad Almasri; eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED districtcoolingrequirements

Mohammad,
You will keep the same the same system from step 1 to step 2 - fan coils with hot water boiler - per Table 3 in the DES guidelines. In step 2, you will create a minimally compliant cooling plant based on Appendix G modeling parameters and attach the fan coils to the plant.

Sam
--
Sam Mason
Atelier Ten


-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mohammad Almasri
Sent: Wednesday, July 07, 2010 8:38 AM
To: eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED district coolingrequirements

Hi all,

I Am working now on a Residential tower supplied by a district cooling plant . The proposed design completed as per the LEED required treatment of district cooling . and two model performed (one with virtual chillers and the other one with chilled water meter to reflect the chilled water cost).

The problem that I have now is in the baseline.

In step one (modeled as cost neutral), the document say that the system will be based on table 3 instead of ASHRAE appendix G , system 2 (FCU will be use instead of PTHP).

Now for step two , what the system will be ; it should be a PTHP or a  FCU with a chillers ? 

Please I need your advice .

Best regards,

Mohammad Al-Masri
Simulation Engineer
CAPM,LEED AP BD+C





_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG

________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The service is powered by MessageLabs. For more information on a proactive anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email ______________________________________________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG



More information about the Equest-users mailing list