[Equest-users] Baseline Modeling as per LEED districtcoolingrequirements
Heather.Hardie-Hill at CH2M.com
Heather.Hardie-Hill at CH2M.com
Fri Jul 9 15:39:16 PDT 2010
I just went through a review process for this!
I initially interpreted it the same way the Cam says below however the LEED reviewer disagreed with me and said I should model it as Sam describes below.
I think the catch is this: on page 6 it says " For such projects the secondary equipment within the building is modeled as described in table 3 above (i.e., the same way as in step 1" it also says "The proposed case modeling requirements differ from those in ASHRAE 90.1-2004 Appendix G; however, the baseline case is modeled as instructed in Appendix G."... I think what this means is that the baseline models should be the same in both case 1 and case 2... and everything should be modeled as described in appendix G except the specific type of system as listed in table 3.
if the above sounds confusing feel free to call me.
Heather Hardie-Hill
EIT, LEEDTM AP
Advanced Design and Simulation
CH2M HILL
Industrial & Advanced Technologies
2020 SW Fourth Ave
Portland, OR 97201
ph: (503).872.4509
e: heather.hardie-hill at ch2m.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Cam Fitzgerald
Sent: Thursday, July 08, 2010 9:11 AM
To: Sam Mason; Mohammad Almasri; eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED districtcoolingrequirements
All:
I hate to disagree with Sam's response, but on page 6 of the USGBC DES document the description of the Model for Step 2 states, "The proposed case modeling requirements differ from those in ASHRAE 90.1-2004 Appendix G; however, the baseline case is modeled as instructed in Appendix G." So for step 2 the baseline HVAC systems for the residential spaces would be PTHP, not AHU's as required for step 1.
Hope this helps!
Cam S. Fitzgerald, PE, LEED AP
Energy Opportunities, LLC
a 7group company
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sam Mason
Sent: Wednesday, July 07, 2010 9:50 AM
To: Mohammad Almasri; eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED districtcoolingrequirements
Mohammad,
You will keep the same the same system from step 1 to step 2 - fan coils with hot water boiler - per Table 3 in the DES guidelines. In step 2, you will create a minimally compliant cooling plant based on Appendix G modeling parameters and attach the fan coils to the plant.
Sam
--
Sam Mason
Atelier Ten
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mohammad Almasri
Sent: Wednesday, July 07, 2010 8:38 AM
To: eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED district coolingrequirements
Hi all,
I Am working now on a Residential tower supplied by a district cooling plant . The proposed design completed as per the LEED required treatment of district cooling . and two model performed (one with virtual chillers and the other one with chilled water meter to reflect the chilled water cost).
The problem that I have now is in the baseline.
In step one (modeled as cost neutral), the document say that the system will be based on table 3 instead of ASHRAE appendix G , system 2 (FCU will be use instead of PTHP).
Now for step two , what the system will be ; it should be a PTHP or a FCU with a chillers ?
Please I need your advice .
Best regards,
Mohammad Al-Masri
Simulation Engineer
CAPM,LEED AP BD+C
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The service is powered by MessageLabs. For more information on a proactive anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email ______________________________________________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100709/7716defe/attachment-0001.htm>
More information about the Equest-users
mailing list