[Equest-users] Creating a Proposed case model in eQUEST
Kelsey VanTassel
KVanTassel at sustaineng.com
Fri Jul 9 10:44:06 PDT 2010
Hi Derek,
Here are the short answers to your questions.
1. I've used Design Development Wizard to set up the base case model, but for the proposed case, I think I just need to switch to the Detailed Data Edit and modify the inputs, right ? Both design cases shall be in the same file, right ?
Yes, you can usually put both proposed and baseline cases in the same model by using parametric runs in Detailed mode.
1. If the previous step is right, then how to restore the previous modifications from Detailed Data Edit if I want to switch between Wizard Data Edit and Detailed Data Edit modes and like to keep all the changes made in Detailed Data Edit mode ?
Once you make changes in Detail mode, you don't go back to Wizard mode. You can do everything in Detail mode that you can do in Wizard, plus lots more, it's just that the Wizard helps you set things up that would otherwise be tedious (such as geometry and schedules). I always save a copy of the file before switching to Detail mode, that way I can flip back and forth between Wizard and Detail mode in that copy without worrying about wiping out the edits I make in Detailed mode in my working file.
Kelsey Van Tassel
Mechanical Engineer | kvantassel at sustaineng.com<mailto:kvantassel at sustaineng.com>
608.836.4488 ext. 20 | Fax: 608.836.4477
Sustainable Engineering Group
901 Deming Way, Suite 201
Madison, WI 53717
www.sustaineng.com<http://www.sustaineng.com/>
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Derek Huang
Sent: Friday, July 09, 2010 12:25 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Creating a Proposed case model in eQUEST
Hi all,
I have two questions when modeling the proposed case:
1. I've used Design Development Wizard to set up the base case model, but for the proposed case, I think I just need to switch to the Detailed Data Edit and modify the inputs, right ? Both design cases shall be in the same file, right ?
2. If the previous step is right, then how to restore the previous modifications from Detailed Data Edit if I want to switch between Wizard Data Edit and Detailed Data Edit modes and like to keep all the changes made in Detailed Data Edit mode ?
I'm new in using eQUEST and looking for your expertise.
Thanks,
Derek Huang, LEED AP, CPD
Mechanical Engineer
[cid:image001.jpg at 01CB1F64.6B3076C0]
97 E. Brokaw Road, No 300
San Jose, CA 95112
Direct: 408 487-1305
Fax: 408 436-1511
www.atce.com<http://www.atce.com/>
derek.huang at atce.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100709/2fcd7dcb/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2266 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100709/2fcd7dcb/attachment-0002.jpg>
More information about the Equest-users
mailing list