[Equest-users] Data Center modeling

Bruce Easterbrook bruce5 at bellnet.ca
Fri Jul 9 16:49:19 PDT 2010


By default equest will assign a ahu system to each floor.  Save a copy 
of the files, PD2, INP, and open the copied project.  On the action tab 
to the left click building creation wizard, ignore the warnings and go 
back, you have a disposable copy right?  Get to the project navigator 
tab.  If you have everything done right you will have your zones under 
the building shell components and under the air side system types you 
from the sound of it you will have HVAC system 1.  You can create your 
new systems using the tab below.  Create what ever systems you need.  
Press finish.  Get into your waterside HVAC tab, it is better explained 
as your system tab.  Look down on the left in your component tree and 
you will see air-side systems.  All you ahu's should be there.  Just cut 
and paste your zones out of HVAC system 1 into the air handlers you want 
them in.  If you empty HVAC 1 of zones delete it.  Ideally you should 
now have all your zones where you want them.  If not save again, go back 
into the building creation wizard and try again.  Good luck.
Bruce Easterbrook P.Eng.
Abode Engineering

On 09/07/2010 07:09 PM, Derek Huang wrote:
>
> Hi all,
>
> I'm working on a energy model for a data center in Seattle. The data 
> center is served by 10 packaged rooftop units. The adjacent 
> Transformer rooms, UPS room and RO room are conditioned by transfer 
> air from the data center. I actually divide the data center, the 
> transformer room and RO room into 10 average pieces so each roof 
> packaged serves (4) areas and these areas are not connected together. 
> So in DD Wizard mode under Zone Pattern (page 2 of 25), I outline (4) 
> different spaces (not connected together) as a group. The program then 
> assigned one system for each area even though I have assigned one 
> system for each Zone Group in page 14 of 25. How could that be ?
>
> Thanks,
>
> **Derek Huang, LEED AP, CPD **
>
> **Mechanical Engineer******
>
> 97 E. Brokaw Road, No 300
>
> San Jose, CA 95112
>
> *Direct*: 408 487-1305
>
> *Fax:*      408 436-1511
>
> www.atce.com <http://www.atce.com/>
>
> derek.huang at atce.com
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>    
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100709/c3475205/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2266 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100709/c3475205/attachment-0002.jpeg>


More information about the Equest-users mailing list