[Equest-users] Baseline Modeling as per LEEDdistrictcoolingrequirements
Mohammad Almasri
malmasri at ems-int.com
Sat Jul 10 23:05:20 PDT 2010
Thanks for all of you , your feedback was very helpful
Masri_new
From: Sam Mason [mailto:sam.mason at atelierten.com]
Sent: Saturday, July 10, 2010 1:40 AM
To: Heather.Hardie-Hill at CH2M.com; cam at energyopportunities.com;
malmasri at ems-int.com; eQUEST-users at onebuilding.org
Subject: RE: [Equest-users] Baseline Modeling as per
LEEDdistrictcoolingrequirements
Thanks for the response with a real project outcome. The sentence Heather
highlights below is my reasoning for keeping fan coils in both cases.
Hopefully the new DES guidelines will provide a more clear path for this
type of modeling (Through the grapevine it is drafted and awaiting release).
Sam
--
Sam Mason
Atelier Ten
From: Heather.Hardie-Hill at CH2M.com [mailto:Heather.Hardie-Hill at CH2M.com]
Sent: Friday, July 09, 2010 6:39 PM
To: cam at energyopportunities.com; Sam Mason; malmasri at ems-int.com;
eQUEST-users at onebuilding.org
Subject: RE: [Equest-users] Baseline Modeling as per
LEEDdistrictcoolingrequirements
I just went through a review process for this!
I initially interpreted it the same way the Cam says below however the LEED
reviewer disagreed with me and said I should model it as Sam describes
below.
I think the catch is this: on page 6 it says " For such projects the
secondary equipment within the building is modeled as described in table 3
above (i.e., the same way as in step 1" it also says "The proposed case
modeling requirements differ from those in ASHRAE 90.1-2004 Appendix G;
however, the baseline case is modeled as instructed in Appendix G."... I
think what this means is that the baseline models should be the same in both
case 1 and case 2... and everything should be modeled as described in
appendix G except the specific type of system as listed in table 3.
if the above sounds confusing feel free to call me.
Heather Hardie-Hill
EIT, LEEDTM AP
Advanced Design and Simulation
CH2M HILL
Industrial & Advanced Technologies
2020 SW Fourth Ave
Portland, OR 97201
ph: (503).872.4509
e: heather.hardie-hill at ch2m.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
<mailto:equest-users-bounces at lists.onebuilding.org>
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Cam
Fitzgerald
Sent: Thursday, July 08, 2010 9:11 AM
To: Sam Mason; Mohammad Almasri; eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED
districtcoolingrequirements
All:
I hate to disagree with Sam's response, but on page 6 of the USGBC DES
document the description of the Model for Step 2 states, "The proposed case
modeling requirements differ from those in ASHRAE 90.1-2004 Appendix G;
however, the baseline case is modeled as instructed in Appendix G." So for
step 2 the baseline HVAC systems for the residential spaces would be PTHP,
not AHU's as required for step 1.
Hope this helps!
Cam S. Fitzgerald, PE, LEED AP
Energy Opportunities, LLC
a 7group company
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
<mailto:equest-users-bounces at lists.onebuilding.org>
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sam Mason
Sent: Wednesday, July 07, 2010 9:50 AM
To: Mohammad Almasri; eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED
districtcoolingrequirements
Mohammad,
You will keep the same the same system from step 1 to step 2 - fan coils
with hot water boiler - per Table 3 in the DES guidelines. In step 2, you
will create a minimally compliant cooling plant based on Appendix G modeling
parameters and attach the fan coils to the plant.
Sam
--
Sam Mason
Atelier Ten
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
<mailto:equest-users-bounces at lists.onebuilding.org>
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mohammad
Almasri
Sent: Wednesday, July 07, 2010 8:38 AM
To: eQUEST-users at onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling as per LEED district
coolingrequirements
Hi all,
I Am working now on a Residential tower supplied by a district cooling plant
. The proposed design completed as per the LEED required treatment of
district cooling . and two model performed (one with virtual chillers and
the other one with chilled water meter to reflect the chilled water cost).
The problem that I have now is in the baseline.
In step one (modeled as cost neutral), the document say that the system will
be based on table 3 instead of ASHRAE appendix G , system 2 (FCU will be use
instead of PTHP).
Now for step two , what the system will be ; it should be a PTHP or a FCU
with a chillers ?
Please I need your advice .
Best regards,
Mohammad Al-Masri
Simulation Engineer
CAPM,LEED AP BD+C
_______________________________________________
Equest-users mailing list
<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The service is powered
by MessageLabs. For more information on a proactive anti-virus service
working around the clock, around the globe, visit:
<http://www.star.net.uk> http://www.star.net.uk
________________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit <http://www.messagelabs.com/email>
http://www.messagelabs.com/email
______________________________________________________________________
_______________________________________________
Equest-users mailing list
<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.830 / Virus Database: 271.1.1/2988 - Release Date: 07/07/10
21:38:00
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100711/802605ee/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 16157 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100711/802605ee/attachment-0002.jpeg>
More information about the Equest-users
mailing list