You can model smaller time periods than 1 year -- I believe 1 day is the 
shortest.  You can also create hourly reports which will show you what 
is happening on an hourly basis.

In the detailed interface -

On the "Project & Site" Tab under Simulation Options you can specify a 
simulation period other than "Entire Year" by entering a start and end date.

To create hourly reports you first create an hourly report block which 
defines what variables you wish to report -- 1 block for each variable 
type.  You then assign all applicable report blocks to the hourly 
report.  Note that you can also define an hourly report schedule to 
define what period the annual report is generated for.  By default it is 
generated for the whole year but you could specify a single day or hour 
by refining the hourly report schedule.

I hope this will give you what you require.

Brian

Matthew Gustafson wrote:
> Hello eQuest users,
>
> I am a new employee at an engineering consulting firm and am looking 
> for some insight into using eQuest to complete a project that was 
> asked of me.  I have been given a generic rectangle building, modeled 
> it with the appropriate fenestration and materials, and want to 
> conduct trials on it.  I want to use eQuest to simulate the solar 
> effect on the building _at a particular hour on a particular day of 
> the year_ (say, 9am June 21st.)  I am wondering if this is possible, 
> as all the results I have obtained so far from the program refer to 
> monthly or annual figures.  Can someone help me out?
>
> -- 
> Matt
> Marquette University '10
> matthew.n.gustafson at gmail.com <mailto:matthew.n.gustafson at gmail.com>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>   
> ------------------------------------------------------------------------
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com 
> Version: 9.0.830 / Virus Database: 271.1.1/2998 - Release Date: 07/12/10 02:36:00
>
>   

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100712/e64c8594/attachment-0002.htm>


More information about the Equest-users mailing list