[Equest-users] Interpretation of Appendix G3.1.2.2 for unmet hours
Dakota Kelley
dakotak at teliospc.com
Tue Jul 13 12:14:07 PDT 2010
My experience has always been that the 50-hour difference is applied separately to heating and cooling hours, so the Difference column in the example below would be out of compliance. The 300-hour limit is applied to each model, so the Difference row in the example would be in compliance.
To reduce Baseline unmet hours, I prefer to leave the cooling/heating coil factors as set by Appx G but gradually increase the minimum CFM/SQFT for the affected zones. I agree that is theoretically possible to adjust sizing factors to eliminate unmet hours, but I argue against this approach in my long-winded discussion of this topic below:
http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-January/003024.html
(See sections 5.b.i and 5.b.ii)
I would apply this approach to your Baseline heating and Proposed cooling air flows to achieve compliance.
Thanks,
DAKOTA KELLEY
Project Designer | Energy Analyst
Office: 214.744.6199
Cell: 214.280.3825
Fax: 214.744.0770
http://www.teliospc.com <http://www.teliospc.com/> 3535 Travis St. Suite 115
dakotak at teliospc.com Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers. Any
distribution or other use is strictly prohibited. Copyright © 2009 Telios Corporation.
From: Patrick J. O'Leary, Jr. [mailto:poleary1969 at gmail.com]
Sent: Tuesday, July 13, 2010 1:35 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Interpretation of Appendix G3.1.2.2 for unmet hours
i've wondered that before. i had a review comment several years ago on a leed 2.1 project where the reviewer disagreed with the concept that the overall unmet load hours were fine as i had a spread similar to yours in the heating or cooling unmet hours. i ended up increasing cmf and/or capacity until they were more in line with each other.
i never did receive a better clarification though, and the 90.1 user manuals only show an example with 0 unmet hours so it is pretty useless in that regard.
On 7/13/10 11:28 AM, Brett Fero wrote:
Has anyone received LEED reviewer comments regarding the fine-line interpretation of Appendix G3.1.2.2 for unmet hours.
I think I meet the criteria as shown in the table below.
The unmet loads in either model is less than 300.
The unmet loads of the proposed building does not exceed the Baseline building by more than 50.
There does not appear to be a requirement regarding the breakdown of heating and cooling unmet hours.
I know I could tweak the over-sizing factors, but am I correct in thinking that these results satisfy AppendixG3.1.2.2 for unmet hours?
Brett Fero, P.E., LEED AP
RobsonWoese Inc.
Syracuse, NY 13212
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100713/95a49cd1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 2278 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100713/95a49cd1/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100713/95a49cd1/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2143 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100713/95a49cd1/attachment-0002.jpeg>
More information about the Equest-users
mailing list