These are the steps I suggest you follow to complete the proposed building and the baseline building models most efficiently:
1) Model the proposed building first. Do everything you can in wizard. Keep a copy of the model at this stage so that you can easily go back to this state of your model if necessary.
2) Save two new copies of your model- one for the proposed model to be completed in the detailed editor and one for the baseline model.
3) Complete the proposed model in detail editor
4) Go back to the model you saved in step 2 of this process as the baseline model and change your selections in the wizard to comply with ASHRAE 90.1. This is quicker and easier than changing all the values manually.Keep a copy of the model at this stage so that you can easily go back to this state of your model if necessary.
5) Save a new copy of the baseline model and complete it in the detailed editor. 
This process allows you to do everything you can in the wizard for both the baseline and proposed building models. It also helps to ensure that schedules and other aspects shared by the two buildings are modeled the same as required by ASHRAE 90.1. 
I hope this helps,
Paul
Paul Buchheit 
Mechanical Engineer
EESI
phone: 541-754-1062
fax: 541-753-3948
paul.buchheit at eesinet.com
  ----- Original Message ----- 
  From: Peter Hillermann 
  To: 'Omar Katanani' ; equest-users at lists.onebuilding.org 
  Sent: Friday, June 11, 2010 9:26 AM
  Subject: Re: [Equest-users] Baseline Modeling
  Omar,
   
  You need to start with the baseline then enter you efficient values. Yes you need to enter ASHRAE standards manually.
   
  Thanks,
   
  PETER HILLERMANN
   
  peterh at westallarchitects.com
   
  westall
  architects
  3404 pierce drive
  chamblee, georgia 30341
   
  o 770.458.4113
  f  770.458.5352
  c 678.898.2936
   
  westallarchitects.com
   
   
   
  From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar Katanani
  Sent: Friday, June 11, 2010 11:48 AM
  To: equest-users at lists.onebuilding.org
  Subject: [Equest-users] Baseline Modeling
   
  Dear all,
   
  I am modeling a school using eQUEST. I have entered the values corresponding to the proposed building (like the specifications given). I would like to model the baseline building according to ASHRAE 90.1 standard. 
  Do I have to change the U-values, HVAC strategy, Window/wall ratio, and the other stuff manually? That is, shall I open the ASHRAE standard and start changing all values one-by-one? The ASHRAE Standard 90.1 isn't recognized by eQUEST such that it can create the baseline case alone? That would save a lot of time!
   
  Best regards,
  Omar
  ___________________________
  Omar Katanani
  Sustainable Design Engineer
  Email: omar at ecoconsulting.net
   
  EcoConsulting (Lebanon)
  Chawkatly Building (Valli & Valli), 6th floor
  Charles Helou Street, Saifi District
  Beirut, Lebanon   
  Mobile:    +961 (0) 3 045 045
   
  EcoConsulting (UK) Ltd
  28 Marshalsea Road
  London, SE1 1HF
  Tel:  +44 (0) 207 939 0989
  Fax:  +44 (0) 207 939 0981
  Website: www.ecoconsulting.net
   
   
   
   
   
   
   
------------------------------------------------------------------------------
  _______________________________________________
  Equest-users mailing list
  http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
  To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/e26bd9b8/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/e26bd9b8/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/e26bd9b8/attachment-0001.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/e26bd9b8/attachment-0003.jpeg>
    
    
More information about the Equest-users
mailing list