[Equest-users] Baseline Modeling
Nick Caton
ncaton at smithboucher.com
Fri Jun 11 11:10:55 PDT 2010
I'd like to highlight this: The workflow process Paul bulleted below is
something I wish I had in front of me when I got started with eQuest,
and is now the exact process I am following for LEED projects. Anyone
aspiring to begin using eQuest for baseline/proposed modeling should
either print this out or commit it to memory.
There's a lot of time to be saved, in my experience, by starting with
the proposed design and then creating the baseline off of that, rather
than vice versa.
On a related note, I wonder if there's any feasible way to flag
submissions to the mailing lists in a way that they are reviewed by the
DOE2/eQuest developers for inclusion in future program
documentation/help files?
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul
Buchheit
Sent: Friday, June 11, 2010 12:23 PM
To: Peter Hillermann; 'Omar Katanani';
equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline Modeling
Hello Omar,
These are the steps I suggest you follow to complete the proposed
building and the baseline building models most efficiently:
1) Model the proposed building first. Do everything you can in wizard.
Keep a copy of the model at this stage so that you can easily go back to
this state of your model if necessary.
2) Save two new copies of your model- one for the proposed model to be
completed in the detailed editor and one for the baseline model.
3) Complete the proposed model in detail editor
4) Go back to the model you saved in step 2 of this process as the
baseline model and change your selections in the wizard to comply with
ASHRAE 90.1. This is quicker and easier than changing all the values
manually.Keep a copy of the model at this stage so that you can easily
go back to this state of your model if necessary.
5) Save a new copy of the baseline model and complete it in the detailed
editor.
This process allows you to do everything you can in the wizard for both
the baseline and proposed building models. It also helps to ensure that
schedules and other aspects shared by the two buildings are modeled the
same as required by ASHRAE 90.1.
I hope this helps,
Paul
Paul Buchheit
Mechanical Engineer
EESI
phone: 541-754-1062
fax: 541-753-3948
paul.buchheit at eesinet.com
----- Original Message -----
From: Peter Hillermann <mailto:e190984026 at exchange.1and1.com>
To: 'Omar Katanani' <mailto:omar at ecoconsulting.net> ;
equest-users at lists.onebuilding.org
Sent: Friday, June 11, 2010 9:26 AM
Subject: Re: [Equest-users] Baseline Modeling
Omar,
You need to start with the baseline then enter you efficient
values. Yes you need to enter ASHRAE standards manually.
Thanks,
PETER HILLERMANN
peterh at westallarchitects.com
westall
architects
3404 pierce drive
chamblee, georgia 30341
o 770.458.4113
f 770.458.5352
c 678.898.2936
westallarchitects.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Friday, June 11, 2010 11:48 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Modeling
Dear all,
I am modeling a school using eQUEST. I have entered the values
corresponding to the proposed building (like the specifications given).
I would like to model the baseline building according to ASHRAE 90.1
standard.
Do I have to change the U-values, HVAC strategy, Window/wall
ratio, and the other stuff manually? That is, shall I open the ASHRAE
standard and start changing all values one-by-one? The ASHRAE Standard
90.1 isn't recognized by eQUEST such that it can create the baseline
case alone? That would save a lot of time!
Best regards,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Chawkatly Building (Valli & Valli), 6th floor
Charles Helou Street, Saifi District
Beirut, Lebanon
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
________________________________
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/2cb2ce8d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/2cb2ce8d/attachment-0006.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/2cb2ce8d/attachment-0007.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: image003.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/2cb2ce8d/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/2cb2ce8d/attachment-0008.jpeg>
More information about the Equest-users
mailing list