In my eQuest adventures i have come across the same thing.  I created a
model and assigned a VAV system to the whole building.  I got one plenum
space per shell.  Then i created a heat pump system that had "system per
zone" default and it created individual plenums.  I think it depends on the
selection of the system and whether it is system per zone/floor/shell/etc.
To recreate them, i just used the system per zone in the wizard, and in the
DD edit i changed the systems as i saw fit and reassigned zones to the
correct layout.  This is easier to me than creating all those spaces, and
then creating all the walls, and then creating all the thermal zones.
Hope this helps a little,
Rob
On Thu, Jun 24, 2010 at 2:32 PM, Nick Caton <ncaton at smithboucher.com> wrote:
>  Connor,
>
>
>
> For a 90.1 baseline/proposed comparison scenario… I’m not certain whether a
> “combined plenum” in one case is acceptable.  A strict reading of Appendix G
> would lead me to say “no,” but if all plenum zones are generally
> unconditioned spaces without systems, the only difference in modeled
> behavior should be the thermal lag/buffer between adjacent plenum zones from
> the partition constructions (assuming the wizards don’t make “air” type wall
> surfaces when generating individual plenums…).  That would probably not be
> significant in many cases.  It might make a significant difference if you
> have core/perimeter terminal units using the plenum as a return air path I
> suppose…
>
>
>
> The wizards are frankly cryptic in how they generate plenums for your
> spaces – I think it involves whether you have a “system per zone” assigned
> to the shell…  perhaps zone group definitions play a role, not sure…  This
> has led me into the same situation, with two comparative models having
> different plenum layouts.
>
>
>
> I do not know of any easy/fast way to recreate or a ton of plenum zones and
> their associations/surfaces between two complex models, when they’ve been
> combined into one.  This is the sort of things that’s scattered throughout
> an .inp file, so it wouldn’t be something easy to just copy-paste…  if it’s
> an option and you have the time, I would advise trying to wrangle the
> wizards into creating the same plenum configuration in both models, but it
> would require some guesswork to figure out how!
>
>
>
> ~Nick
>
>
>
> [image: cid:489575314 at 22072009-0ABB]**
>
> * *
>
> *NICK CATON, E.I.T.***
>
> PROJECT ENGINEER
>
> 25501 west valley parkway
>
> olathe ks 66061
>
> direct 913 344.0036
>
> fax 913 345.0617
>
> *Check out our new web-site @ *www.smithboucher.com* *
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jansen, Connor
> *Sent:* Thursday, June 24, 2010 12:51 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Recreating Plenum Spaces
>
>
>
> Hello All,
>
>
>
> I’m looking for some insight on how plenum zones may or may not affect my
> modeling outcome.
>
>
>
> The building in question has changed from a 90.1 baseline system type 6
> Packaged VAV to a system 4 Packaged Single zone. The model is currently
> using a single plenum zone for the entire floor. I’ve noticed in the past
> (correct me if I’m wrong) that when assigning spaces to HVAC systems in the
> wizard it will output individual plenum spaces for corresponding zones when
> using single zone HVAC systems and a combined plenum space when using
> multizone systems.
>
>
>
> Is it necessary to recreate the individual plenums in the detailed mode if
> I switch to single zone systems? If so is there a simple way of doing this?
>
>
>
> Thank you for the help.
>
>
>
> Regards,
>
>
>
> Connor
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-- 
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100624/a14d4f3d/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list