[Equest-users] ASHRAE Baseline EUI
    Nick Caton 
    ncaton at smithboucher.com
       
    Mon Mar  1 07:58:55 PST 2010
    
    
  
I was just suggesting the same thing...
 
E-star's target finder is not the most crystal-clear of tools, but does
pretty much deliver what you're looking for.
 
Some nuances:
 
Choosing various energy sources (i.e. Grid Electricity vs. Bituminuous
Coal) does have an effect on the CO2 emission calculations, but not on
the resulting target/average energy results.  Those energy figures are
not affected by the region your project is in, so it would be a stretch
to say you're getting a baseline of "Warehouses in Chicago."  You will
however get a baseline btu/sf/yr that corresponds with your building
occupancy and size.  
 
For further reading, I've attached a document I received on request from
the EPA, which details how source energy is dealt with currently... it's
informative if you need/want to understand what exactly the e-star
target finder tool is doing with regards to those "source energy" inputs
- which can have somewhat unintuitive effects on the results that are
churned out.
 
~Nick
 
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David S
Eldridge
Sent: Monday, March 01, 2010 9:48 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ASHRAE Baseline EUI
 
ENERGY STAR target finder? 
 
David
http://www.grummanbutkus.com
 
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Skelton, Paul
Sent: Monday, March 01, 2010 9:21 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] ASHRAE Baseline EUI
 
All,
 
I have developed a baseline building and calculated its energy use index
(EUI), total source building btu use divided by building square footage,
and I am curious to compare it to other models.  Obviously since many
users on this list are from very different climate zones, we will get
some varying answers.  However, I would still be interested to see what
kind of use different buildings are characterized by, especially in
Michigan.  Or, if any of you know a resource that I can use to reference
this type of information, I'd be grateful.
 
Thanks!
 
Paul Skelton
Integrated Design Solutions
Architecture, Engineering, Interiors & Technology
888 West Big Beaver, Suite 200
Troy, Michigan 48084
tel:   248.823.2171
fax: 248.823.2200
www.ids-troy.com <http://www.ids-troy.com/> 
Celebrating 10 Years.  Expect the Exceptional. 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100301/a747b918/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100301/a747b918/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: site_source_20090831.pdf
Type: application/octet-stream
Size: 121089 bytes
Desc: site_source_20090831.pdf
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100301/a747b918/attachment-0002.obj>
    
    
More information about the Equest-users
mailing list