[Equest-users] GSHP with 3.61 and 3.63b.  PV power usage
    eric wang 
    shaojieworld2006 at yahoo.com
       
    Thu Mar  4 13:39:28 PST 2010
    
    
  
Varkie,
 
Maybe you need to check the depth of vertical well and num of identical well fields under Ground Loop Heat Exchanger Properties. Also, you can check min and max ground loop temperature in DOE2 PS-H report.
 
Hope it helps! 
Shaojie (Eric) Wang
Sr. Systems Engineer
PE, LEED AP
ClimateMaster, Inc.
--- On Thu, 3/4/10, Varkie C Thomas <thomasv at iit.edu> wrote:
From: Varkie C Thomas <thomasv at iit.edu>
Subject: [Equest-users] GSHP with 3.61 and 3.63b. PV power usage
To: "Equest Users Mailing List" <equest-users at lists.onebuilding.org>
Date: Thursday, March 4, 2010, 3:44 PM
I tried to run 3,63b with a GSHP input file that ran with 3.61.  I got the following caution and error messages shown below and the SIM reports stopped after loads.  The BDL file shows that the program ran all the way through with no error messages.  How do I fix the input for 3.63b so that this 3.61 input file runs?
 **CAUTION**********************************************************************
             In curve: CYCLING-PUMP                     the dependent value
             is exceeding the limits.
             Value/Min/Max/First time:          1.015          0.020          1.000   1/ 2/ 8
 
 ***ERROR***********************************************************************
             Ground-loop HX: GROUND-HX-1                     
             is undersized for the load and is producing an extreme
             temperature of   -12F.  Mon/Day/Hr:  1/ 2/ 8
 
How does eQUEST distribute the PV generated power to lights, equipment, cooling, pumps & fans in the BEPS report?  Can the details be viewed in one of the other reports
Varkie
-----Inline Attachment Follows-----
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100304/3c799bd6/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list