I’ve done this only once, but here’s how I went
about it:
You model the chilled beam system as an induction unit (assuming
it s a passive chilled beam). You will need to model it’s OA from a DOAS
system. Since the chilled beam system itself does not use fan energy you will
need to set your kW/cfm at zero. The fan energy gets captured at the air
handler. Now with the lab I was modeling the chilled beam was running on 100%
OA, so this was a valid approach.
If the chilled beam air handler has recirculation air
(return air), this might not be a valid approach.
Vikram Sami,LEED AP
Direct Phone
404-253-1466 | Direct Fax 404-253-1366
LORD, AECK& SARGENTARCHITECTURE
From:equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha
Korber-Gonzalez
Sent: Tuesday, March 09, 2010 1:29 PM
To: wallie padero
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Chilled Beams Modelling
Wallie,
I've never tried this method, but I came across this thread
yesterday when I was perusing the archives for other data...let us know if this
approach is successful for your project.
http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2009-April/001397.html
Pasha
On Tue, Mar 9, 2010 at 7:01 AM, wallie padero <wallie_p at yahoo.com> wrote:
Hi
guys!
Does anyone knows how to model chilled beams in e-quest? What system should i
used?
Thank you so much in advance.
Wallie
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100312/96c2cbce/attachment-0002.htm>
More information about the Equest-users
mailing list