[Equest-users] coordinate errors
    Grando, John 
    JGrando at cosentini.com
       
    Tue Mar 16 06:00:24 PDT 2010
    
    
  
 
Please see the attached screenshot.  The issue I believe you are having is that you are specifying a 15 ft perimeter depth between two walls that aren't 30 ft apart.  The program has a big problem with this and the zoning coordinate system usually gets messed up.  You can go into these spaces, set up the 15 ft perimeter depth like you have now, then on the zoning pattern button, click custom.  A box will show up and select "keep existing zoning", then your zoning screen will appear and you can fix these trouble spots while keeping the rest of the shell with the 15 ft perimeter.
 
John Grando LEED AP| Mechanical Engineer
Phone: 212-615-3705 | Fax: 212-615-3700
jgrando at cosentini.com
Cosentini Associates - A Tetra Tech Company
Two Pennsylvania Plaza - Third Floor - New York, NY 10121
www.cosentini.com
 
-----Original Message-----
From: jredburn at mindspring.com [mailto:jredburn at mindspring.com] 
Sent: Monday, March 15, 2010 5:36 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] coordinate errors
Sirs,
I have a rather complex shape to model and it is giving me fits.  I have leaned a lot of things not to do over the past few days.
I finally got the entire foot print into the program.  Some 18 shells and almost a 1000 vertices.  I also have a long list of errors that tell me there are two vertices with the same coordinates.  The first on my error list is Space E5 and it has 16 vertices,  all of which are unique on the list at the right hand side of the page where I trace the points from my Cadd drawing.  That page has coordinates units in the range of 40 to 70 ft from the orgin, both x and y.
When I click finish from the navigator and the error list comes up, I find 21 vertices on the list and 14 and 16 are the same, except the units are all in the 300 to 400 ft range.
Also, I drew 8 of the shells as a rectangle and stuck three small rectangles on the side of the first one as bay windows.  When I trace them in E Quest with a  N-S orentation they act just fine and the roof will plot quite nicely.  When I rotate the shells in Cadd to fit the main building  and transfer them to E Quest, they throw an error when I try to put a roof on them.
NOTICE OF CONFIDENTIALITY
This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof.  In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law.  If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission.  Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege.  If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
-------------- next part --------------
A non-text attachment was scrubbed...
Name: screenshot.JPG
Type: image/jpeg
Size: 64107 bytes
Desc: screenshot.JPG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100316/d7526077/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list