Mike,
In a word, no. The defaults you see are more likely geared toward Title 24
compliance since the development of eQUEST is subsidized through the Ca PUC.
First of all you need to figure out which version of ASHRAE 90.1 you want to
comply with, let's say it's the 2007 version. You then need to read through
Appendix G, at the back of the Standard. There are step by step requirements
in it telling you how to show compliance. There is also a User's Guide you
can purchase through ASHRAE which I would recommend.
Never assume anything when you are using eQUEST. You can always right on a
field and read about it using Item Help. You can also read user manuals and
dictionaries. Some of us have been doing this work for years and years and
still know we have a lot to learn. It's a complex model which adheres to the
GIGO rule. It won't always tell you when you have put garbage in either.
Good luck!
Caqrol
On Sat, Mar 20, 2010 at 10:32 AM, <mike584595 at aol.com> wrote:
> All:
>
> In an earlier e-mail, I mentioned that I had modeled my first building and
> that the project had gone very well.  I built the model by entering data
> that reflected the existing building.  The results were impressive since the
> estimated annual energy costs were $47,274 and the actual energy costs were
> $48,536.
>
> The building was built in 1998 and I know the designers.  I know that its
> design doesn't comply with ASHRAE 90.1 parameters.  So, if I want
> to estimate the energy costs of this building built to comply with ASHRAE
> 90.1, what do I do?  I noticed as I was entering the building parameters
> originally that the fields were populated with default values.  Are these
> the values that would comply with ASHRAE 90.1?  If I simply ran the
> simulation based on the program default values, would that generate the
> estimated annual energy costs of this building had it been built to comply
> with ASHRAE 90.1?
>
> Thanks,
>
> Mike Porter
> Porter Brothers, Inc.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100320/58d0d6cf/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list