[Equest-users] ground-source heat pump with gas backup
Bishop, Bill
wbishop at pathfinder-ea.com
Tue May 18 07:18:51 PDT 2010
Demba,
Here are two options that come to mind:
1.) Add an electric HP-SUPP-SOURCE. Convert the electric use to gas
(by hand calculation, not within eQUEST) and use the furnace AFUE to
account for inefficiency.
2.) Add baseboard heating of type FURNACE. Use OA TEMP control,
create a RESET-RATIO baseboard schedule and adjust the OA temperatures
to minimize daytime operation of the baseboards. You will need to create
an hourly report to see when the baseboards (furnaces) are coming on.
Regards,
Bill
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P May is National Bike Month. Bike to Work Day May 21st.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Demba
Ndiaye
Sent: Tuesday, May 18, 2010 8:29 AM
To: Carol Gardner; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ground-source heat pump with gas backup
Carol,
The building is a school. Operating hours are basically 7am - 4pm. The
furnace operates as a backup only during the day, but at night is the
only one operating to maintain heating setback.
I have two system types: one is a PVAV and one, a PVVT.
I can shut down the pumps through a schedule for night-cycling, but
cannot see how to get only a furnace operating for night-cycling.
Demba.
From: Carol Gardner [mailto:cmg750 at gmail.com]
Sent: Monday, May 17, 2010 8:21 PM
To: Demba Ndiaye
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] ground-source heat pump with gas backup
Hi Demba,
What is the building type and operating schedule? Why the gas furnace as
back up to cycle on only at night?
Carol
On Tue, May 18, 2010 at 12:21 AM, Demba Ndiaye <Demba.Ndiaye at setty.com>
wrote:
Folks,
I have a ground-source heat pump that operates during the day. At night,
the pumps are shut off, and if the space needs heating to maintain the
setback temperature, a gas furnace kicks off.
Said otherwise, only the furnace operates to maintain setback.
How would you model that?
_______________
Demba NDIAYE
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100518/e1d1637b/attachment-0001.htm>
More information about the Equest-users
mailing list