Carol Gardner cmg750 at gmail.com
Fri May 7 13:29:12 PDT 2010


Setting Maximum Heating Rate to 1 Btu/h gets rid of heating. On air-side
hvac zone parameter screen, under heating tab. Change 1 time using your
screen then find it under the spreadsheet option where you can copy and
paste.

Note: you may still see a heating load on SV-A but you should have no
heating energy use.

Another issue comes to mind: how to do this using a schedule so you can have
heat when you want it.

Peace,
Carol

On Fri, May 7, 2010 at 1:13 PM, Paul Brooks <equestpaul at yahoo.com> wrote:

> I am getting a heat load in the middle of the cooling season.  I don't
> believe it.  the system is VAV, chilled water with reheat coils at the boxes
> only.  Office Building in a semi-tropical zone (3).
>
> I understand that I should be able to turn the heat off/make unavailable,
> but the instructions on how seem cryptic.....that or my brain is
> overloaded.  Can someone provide a quick answer ton how to do it?
>
> Thanks!
>
>
>
>