I'd like to echo and add to Andrew's illustration:
I've used this approach often to make wraparound zones/shells in the
past.
Something to note is that Andrew has a vertex highlighted in the
screenshot below which I learned can be a time-saver, so is important to
think about when preparing your CAD reference. Try to make a point to
define a vertex at each corner of the "donut hole," even if you don't
need to to make the shape. This will create a separate
partition/exterior wall where the two "face-to-face" partitions exist,
so that you can easily modify (or delete) them later in detailed as may
be necessary.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Reilman, Andrew
Sent: Tuesday, October 19, 2010 10:44 AM
To: Eddie Corwin; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] (no subject)
You can fake a donut zone though. The vertices just need to be "close".
The picture I attached shows this a little exaggerated.
Regards,
Andrew Reilman, P.E.
Associate
Senior Engineer, LEED(r) AP BD+C
Syska Hennessy Group, Inc.
A member company of SH Group, Inc.
11500 W. Olympic Blvd.,
Suite 680
Los Angeles, CA 90064
Tel: 310.254.3894
Cell: 510-710-4817
Fax: 310.473.7468
Email: areilman at syska.com <mailto:areilman at syska.com>
http://www.syska.com <http://www.syska.com/>
Please consider the environment before printing this e-mail
________________________________
This email and any files transmitted with it are the property of SH
Group, Inc. and are intended solely for the use of the individual or
entity to which they are addressed. The information contained herein may
include trade secrets or privileged or otherwise confidential
information and unauthorized review, forwarding, printing, distributing,
or using such information is strictly prohibited and may be unlawful. If
you received this message in error, or have reason to believe you are
not authorized to receive it, please promptly delete this message and
notify the sender by e-mail.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Eddie
Corwin
Sent: Tuesday, October 19, 2010 8:28 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] (no subject)
You can not make a "Doughnut" zone. you will need to separate the
perimeter zone into two or more zones. Using the "Core/Shell Zoning
pattern that is available in the wizard works well.
________________________________
From: Erik Weiss <ew0187 at gmail.com>
To: equest-users at lists.onebuilding.org
Sent: Tue, October 19, 2010 11:22:08 AM
Subject: [Equest-users] (no subject)
I am creating a 20 floor building and the core is defined. i am trying
to create the zones within the core and the large single zone
surrounding the core. I am unable to create 1 single zone surrounding
the core because the wizard does not allow you to select the same vertex
twice in a single zone. Is there anyway around this
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/11a42ef4/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/11a42ef4/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 19198 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/11a42ef4/attachment-0003.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2443 bytes
Desc: image006.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101019/11a42ef4/attachment-0002.gif>