[Equest-users] Under sized cooling coil
Eddie Corwin
ecorwin at altanova-energy.com
Tue Oct 19 14:25:45 PDT 2010
One quick and easy fix is to increase the sizing factor found in the cooling
tab. Currently you have it set to 1.15. I tried setting it to 2.0, and there
were no more unmet hours.
__________________________________________________________
Eddie Corwin, Energy & Sustainability Engineer
ALTANOVA - www.altanova-energy.com
41-41 24th Street - 4th Floor - Long Island City, NY 11101
T: (347) 410-9049
E: ecorwin at altanova-energy.com
________________________________
From: Brad L. Huff <BradH at BVHis.com>
To: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Tue, October 19, 2010 5:02:26 PM
Subject: [Equest-users] Under sized cooling coil
All,
I am modeling a portion of a 100% outside air lab in a type 5A climate zone. The
area is below ground/has interior walls so there is no fenestration. The system
has two chilled water air handling units and VAV boxes with zone reheat. The two
AHU’s run 24/7 at a constant CFM because the supply air is driven by a required
air change rate per room type.
My problem is:
- I have too many unmet cooling hours when allowing e-Quest to auto-size the
cooling coil capacity of the air handling units
Diagnosis:
- The delta T of the cooling coil never gets above 7 degrees F any day
of the summer.
- e-Quest severely undersized the cooling coils from a design day. (I
have calculated the design day cooling load by hand)
- No warnings in the Sim report
I have tried troubleshooting the system for a couple of days but am unable to
find the reason e-Quest is under sizing the cooling coil capacity. I have
attached the .inp file. Any suggestion are greatly appreciated.
Thank you,
Brad
Brad Huff, E.I.T., Mechanical EngineerI BVH Integrated ServicesI 860.286.9171
tel I860.242.0236 fax I50 Griffin Road South, Bloomfield CT 06002 I
www.bvhis.com