A more accurate approach pertaining to solar gains would be to use separate
perimeter zones for each façade of the building. This may be required for
your baseline model if you are using Appendix G. (See Table G3.1.8.b)
If this doesn’t apply, and you’re certain that the HVAC system is/will be
designed and controlled reflecting one zone per floor, you can make the
perimeter zone “wrap-around” the core. As another poster mentioned, you
can’t make it a “doughnut” shape. I’m not sure if the wrap-around approach
can be done in the wizard or not. You might also approximate the situation
by moving the new vertex off of the first vertex just enough to make the
program run.
By the time you did that, it would probably have been easier (and more
accurate) to make separate perimeter zones for each façade, which the wizard
can definitely do.
David
*
*
*David S. Eldridge, Jr.**, P**.**E**.**, LEED AP BD+C, BEMP, HBDP*
Project Manager
Direct: (847) 316-9224 | Fax: (847) 328-4550
http://www.grummanbutkus.com
*Grumman/Butkus Associates* | 820 Davis Street, Suite 300 | Evanston, IL
60201
Energy Efficiency Consultants and Sustainable Design Engineers
*
*
> -----Original Message-----
> From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-
> bounces at lists.onebuilding.org] On Behalf Of Erik Weiss
> Sent: Tuesday, October 19, 2010 10:22 AM
> To: equest-users at lists.onebuilding.org
> Subject: [Equest-users] (no subject)
>
> I am creating a 20 floor building and the core is defined. i am trying to
> create the zones within the core and the large single zone surrounding the
> core. I am unable to create 1 single zone surrounding the core because the
> wizard does not allow you to select the same vertex twice in a single
zone.
> Is there anyway around this
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-
> USERS-UNSUBSCRIBE at ONEBUILDING.ORG