[Equest-users] Non-vertical windows

Pasha Korber-Gonzalez pasha.pkconsulting at gmail.com
Wed Oct 27 19:39:42 PDT 2010


Yes, you can specify angled walls in DDedit mode.   When you are in DDedit,
find the actual wall that you want to tilt, open the properties window and
you will find an input for the tilt angle.    Be mindful that you will have
to make sure that all other surfaces adjacent to this angled surface are
then adjusted for their geometry so that all the constructions line up as
they should.

pkg

2010/10/27 Marie-Claude Hamelin <marie-claude.hamelin at usherbrooke.ca>

> Hi,
> I am trying to model a building which has a non-vertical structure; the
> walls and windows on the north and south sides are oriented to benefit as
> much as possible from the sun. Is there a way to model an angled wall, or at
> least the windows, for solar gains? Thanks!