[Equest-users] Equest and TRNSYS
Fred Betz
fbetz at aeieng.com
Fri Oct 29 12:08:55 PDT 2010
Cory,
I have integrated eQuest and TRNSYS lots of times.
Create an hourly report in eQuest for your heating load and export it to a .csv file.
I usually convert the eQuest load from Btuh to kJ/hr within excel, but you could use an equation block in TRNSYS.
Use Type9c unformatted data reader from TRNSYS to read the hourly report.
Type9c is located in the tree under: Utility/Data Readers/Generic Data Files/Skip Lines to Start/Free Format
Be careful with the "lines to skip" parameter in Type9c so that it matches the title text in the hourly report .txt file.
Also remember heating load values are supposed to be negative numbers in TRNSYS.
The one caveat with this whole concept is that any over heating or high temps created by your solar thermal system is not translated back to eQuest. Be careful with your control system and verify that you stay within the bounds of eQuest for hot water temperatures to be as realistic as possible.
Fred
Fred Betz PhD., LEED AP
Sustainable Systems Analyst
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com<mailto:fbetz at aeieng.com> | www.aeieng.com<http://www.aeieng.com/>
From: Cory Duggin [mailto:crduggin at gmail.com]
Sent: Thursday, October 28, 2010 4:35 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Equest and TRNSYS
Has anyone ever integrated the load results from a equest model into a TRNSYS model. I have a complete equest model, but I need to use the solar modeling in TRNSYS. I was hoping to have to not remodel and tweak what I already have done in equest in TRNSYS.
--
Cory Duggin, EI
Tennessee Tech University
Graduate Research Assistant
Mechanical Engineering