[Equest-users] Floor Slab F-factor
Jeremy Poling
jpoling at epsteinglobal.com
Thu Sep 9 11:15:03 PDT 2010
The inter-office debate is more on advising our architect on options for
slab insulation using the energy benefits of one option compared to
another. The project having the debate is a large area low-height
building with some spaces similar to a warehouse, so from an envelope
perspective the critical envelope gain/loss surfaces are the Roof and
the Slab.
We arrived at this question for eQuest since the other model used in
house is Trace and Trace uses F-Factor directly for slab-on-grade. For
eQuest, since the guidance on converting F-Factor to U-Factor for use in
eQuest was written in 1998 and was based on DOE2.1E, does eQuest 3.64
still use the same methodology? The question also goes back to a
comment much earlier in the archives on this being an area of eQuest
that should be added in a future revision of eQuest.
Thanks for the help!
JEREMY R. POLING, PE, LEED AP
Associate Vice President,
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.
From: Jonathan Smith [mailto:jsmith at csarchpc.com]
Sent: Thursday, September 09, 2010 7:39 AM
To: Jeremy Poling; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Floor Slab F-factor
Jeremy,
What's the point of contention you're debating?
I would begin with creating a eQuest wizard model simulation that is
representative of the slab-on-grade example(s) given in the article.
Jonathan
From: Jeremy Poling [mailto:jpoling at epsteinglobal.com]
Sent: Wednesday, September 08, 2010 6:58 PM
To: Jonathan Smith; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Floor Slab F-factor
I'm a little tardy joining this thread, but the original write-up was
from the Spring 1998 edition of the "Building Energy Simulation"
newsletter. I am hoping someone can confirm that this is still the
correct method for the latest versions of eQuest and DOE2.2 to solve an
inter-office debate. Thanks!
JEREMY R. POLING, PE, LEED AP
Associate Vice President,
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Jonathan Smith
Sent: Tuesday, June 08, 2010 10:19 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Floor Slab F-factor
All:
The document regarding eQuest perimeter slab heat calculations is
appended to the eQuest Training Workbook. See the link below.
"Underground Surfaces" by Fred Winkelmann (LBNL)
http://doe2.com/download/equest/eQuestTrainingWorkbook.pdf
Jonathan R. Smith AIA LEED(r)AP
40 Beaver Street
Albany, New York 12207
p: 518.463.8068 x268
f: 518.463.8069
www.csarchpc.com <http://www.csarchpc.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/30e6fdda/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 11096 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100909/30e6fdda/attachment-0001.jpeg>
More information about the Equest-users
mailing list