[Equest-users] 90.1 Supply Fan Energy
    M. Shields 
    mshields at fstrategies.com
       
    Wed Apr  6 12:57:24 PDT 2011
    
    
  
I looked at the ACH based on the SV-A system CFM and the volume of the zone
and it does seem high (2-5 ACH), but I let equest calculate the system CFM
for me.
 
I have one system per zone so I specified OA in the zone tab as a overall
CFM rate based on the 62.1 calculations I did.
 
From: Carol Gardner [mailto:cmg750 at gmail.com] 
Sent: Wednesday, April 06, 2011 3:37 PM
To: M. Shields
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] 90.1 Supply Fan Energy
 
Check your cfm/sf number in your systems, that would definitely cause this
if it's set too high. Also what field are you using for your OA ventilaton? 
Carol
On Wed, Apr 6, 2011 at 12:22 PM, M. Shields <mshields at fstrategies.com>
wrote:
Hi all,
 
I am in the process of breaking out the fan energy from my HVAC system per
ASHRAE 2004 G3.1.2.1, following G3.1.2.9.  The amount of energy coming from
my fans seems massive and I'm not sure if that is typical, or if I've messed
something up.  I started by setting the temperature difference of 20 degrees
between supply and desired temp (55/75 cooling and 90/70 for heating) and
specified 62.1-2004 ventilation for outside air.  I then ran equest and used
the SV-A reports to get supply CFM for each system.  From that number I then
used Table G3.1.2.9 to get BHP for each system, which I then converted to kW
using the formula in ASHRAE.  I then took that number and divided by CFM to
get kw/CFM and entered this number on the system->fan tab.  When I go to the
SV-A report the system kW is exactly what I calculated it to be, but the
energy required for my ventilation fans is about the same as my heating and
cooling load combined, which seems outrageous.  
 
Is this typical?  Have I entered it In the wrong way? I would think fan
consumption would typically be a fraction of the actually heating and
cooling energy.  Thanks for any thoughts.
 
____________________________
Michael Shields
Facility Strategies Group, LLC
1012 Market Street, Suite 307
Fort Mill, SC 29708
Phone: 803-493-4507
Fax: 803-548-2511
Email: mshields at fstrategies.com
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-- 
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110406/32f85133/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list