[Equest-users] Difference between wizard and detailed mode
Nick Caton
ncaton at smithboucher.com
Wed Apr 13 14:21:33 PDT 2011
Hey Travis,
What you've currently got is:
- A 60ton unit for each floor's core zone (2 total)
- A series of 5 and 7.5 ton units each serving one perimeter zone (8 total) ß note: cooling capacities appear to have been edited after the wizards
- Total units: 10
- Picture:
It sounds like the desired is to have:
- A 60ton unit for each floor's core zone (2 total)
- 15 ton units each serving two perimeter zones (4 total)
- Total units: 6
To pull this off you need to
1. Go back to wizards
2. Review/Correct the tonnage for the smaller units, as necessary (wizard inputs don't reflect 15 tons all around)
3. Select "system per site" in the first screen of each system (note: you've got "system per zone" selected currently, which assigns one system of the specified sort to each zone in the shell associated... this is the main source of your system quantity issue).
4. Assign the perimeter zones to the appropriate systems (looks like you've already done this correctly, but review to be sure assignments are correct).
When finished and on exiting the DD wizard, you should observe the correct quantity of systems and zone assignments on review of the airside HVAC tab/component tree.
Best of luck!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Travis Rhodes
Sent: Wednesday, April 13, 2011 12:08 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Difference between wizard and detailed mode
Thanks
Travis Rhodes
ENERGY ADVISOR
(916)732-5274
trhodes at smud.org
From: Carol Gardner [mailto:cmg750 at gmail.com]
Sent: Wednesday, April 13, 2011 10:05 AM
To: Travis Rhodes
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Difference between wizard and detailed mode
Hi Travis,
You need to attach the .inp file that this .pd2 file uses, too.
Carol
On Wed, Apr 13, 2011 at 9:56 AM, Travis Rhodes <TRhodes at smud.org> wrote:
I'm trying to set up a really simple 2 story building with 6 rooftop units. Two 60 tons supply cooling only to the core of the two floors and the 4 15 ton units take care of the perimeter. One unit supplies air to two walls on the first floor and another unit takes the other two walls on that floor. This is repeated on the second floor. In the wizard I set it up exactly like this and inputted the performance data for each unit and named each unit but when I go to detailed mode to modify the schedules to reflect the controls of the system it has broken everything out completely different than what I assumed I had set up in the wizard. I've attached the .pd2 file, I don't know if this is sufficient for anyone to look at what I've done.
I appreciate anyone help on this.
Error! Filename not specified.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110413/a73d96e9/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110413/a73d96e9/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 17443 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110413/a73d96e9/attachment-0002.png>
More information about the Equest-users
mailing list