[Equest-users] Humidity control question
    Dakota Kelley 
    dakotak at teliospc.com
       
    Tue Apr 19 14:37:46 PDT 2011
    
    
  
I don’t necessarily see a problem from the info presented, but the complete/correct answer requires more knowledge about your design conditions and system configuration.  From what was explained, it sounds like your 50% RH set point can be maintained with whatever you specified for the cooling LAT.
I would only expect summer reheat if you had to cool below your desired LAT to achieve sufficient dehumidification (or if you had a multi-zone VAV with reheat and had interior zones being overcooled in the summer, but that does not sound like what you’re modeling).  If you’re trying to supply at 55 F but have to cool to a lower temperature to dehumidify, there should be reheat.  Otherwise, coming off the coil at or near 55 F & 90%+ RH is often sufficient for maintaining 50% RH and a dry bulb temperature in the low to mid 70’s.  Note that the reheat does nothing for moisture removal, it simply heats the airstream back up to avoid over cooling the zone.
Plot your design conditions on a psychometric chart and see if they make sense – I’d be happy to help in this regard.  Just send me your supply air, exterior design conditions, and interior design conditions.
Thanks,
[cid:image004.png at 01CBFEB0.1D2CB700]
DAKOTA KELLEY
Project Designer | Energy Analyst
                              Office: 214.744.6199
                              Cell: 214.280.3825
                              Fax: 214.744.0770
http://www.teliospc.com <http://www.teliospc.com/>          3535 Travis St. Suite 115
dakotak at teliospc.com<mailto:dakotak at teliospc.com>            Dallas, TX 75204
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed,
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you
are not the intended recipient, please email the sender immediately, and delete this email from all computers.  Any
distribution or other use is strictly prohibited.  Copyright © 2011 Telios Corporation.
From: Sami, Vikram [mailto:Vikram.Sami at perkinswill.com]
Sent: Tuesday, April 19, 2011 1:37 PM
To: Equest Users Mailing List
Subject: [Equest-users] Humidity control question
So I have an HVAC system setup with a preheat coil, a cooling coil and a heating coil. The humidistat is set to 50%, and it’s a 100% OA system.
I assumed you set the LAT for the cooling coil with the cold deck min leaving temp and then the LAT for the heating coil with the Zone entering min supply temp.
I’m getting curious results though – I get no heating loads in the summer months – which I should get for humidity control. I setup some hourly reports to track the temperature of the air leaving the heating & cooling coils and the dehumidification reheat heat as well as the moisture added or removed from the air for dehumidification. I notice that while the cooling coil & heating coil temps seem to be ok and there is moisture removal reported, there seems to be no energy reported for reheat for humidity control.
What am I missing?
Vikram Sami, LEED AP BD+C
Sustainable Design Analyst
1315 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com<mailto:vikram.sami at perkinswill.com>   www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will.  Ideas + buildings that honor the broader goals of society
Perkins+Will is carbon neutral. Learn more about our 2030 Challenge Estimating + Evaluation<http://2030e2.perkinswill.com/> tool for fossil fuel free buildings
This email and any files transmitted with it are confidential and intended solely for the addressee.  If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/5177f788/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.emz
Type: application/octet-stream
Size: 6649 bytes
Desc: image003.emz
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/5177f788/attachment-0002.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 3500 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110419/5177f788/attachment-0002.png>
    
    
More information about the Equest-users
mailing list