[Equest-users] Chillers in Series inputs
Anthony Hardman
Anthony at GreenEngineer.com
Fri Apr 22 13:55:02 PDT 2011
The keyword "SERIES-SETPT-RAT" to setup chillers in series is still listed
as future in the help files.
Could that be why you're running into trouble?
Anthony Hardman, PE
LEED AP BD&C
Building Performance Analyst
THE GREEN ENGINEER, LLP
Sustainable Design Consulting - Energy Modeling - LEED Project Management
50 Beharrell St
Concord, MA 01742
O: 978/610-2801
C: 720/840-7862
<http://www.GreenEngineer.com> www.GreenEngineer.com
www.linkedin.com/in/ahardman81
http://twitter.com/#!/a_Hardman
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha
Korber-Gonzalez
Sent: Friday, April 22, 2011 2:04 PM
To: James Hansen
Cc: eQUEST Users List; Arunabha Sau
Subject: Re: [Equest-users] Chillers in Series inputs
Thanks Rob & James for your prompt input to my dilemma....after I sent the
email to the list, I went back in my plants to try and make sense why the
secondary wasn't seeing a load--so for a random test I switched the
assignement of the two chillers (just reversed which loops they are on.) and
then ran the sim without errors. That was the good news. I don't have my
head around the logic of why that worked on the first try, but maybe I was
having some dislexia-input moments and spec'd my chiller conditions
backwards (i.e. high chiller & low chiller in the series).
Since it has ran I noticed an immediate reduction in chiller energy use, but
I haven't yet verified if the reduction is realistic and if there are any
other QC error type things to verify that this approach is indeed modeling
the chiller temps in series. I don't think I will mess with custom chiller
curves at this point because this project model is only SD. Therefore I
won't be held to any compliance reviews and strict performance results...at
least not at this point in time.
I'll try to send feedback when I can verify that this is a valid input
option for chillers in series, or if it holds no water at all...
Cheers,
Pasha
On Fri, Apr 22, 2011 at 12:18 PM, James Hansen <JHANSEN at ghtltd.com> wrote:
Most manufacturers will give you a "single chiller" performance curve for
the two chillers in series. I typically just make custom chiller curves to
represent series chillers as a single chiller. If a designer creates
valving that allows water to NOT have to flow through both chillers during
low load operation, this gets a little tricky, and I end up averaging the
delta P across the chillers to represent partial operation thru both
chillers and partial operation thru a single chiller. No easy way to do
this.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
<http://www.ghtltd.com/> www.ghtltd.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob Hudson
Sent: Friday, April 22, 2011 2:15 PM
To: Pasha Korber-Gonzalez
Cc: eQUEST Users List; Arunabha Sau
Subject: Re: [Equest-users] Chillers in Series inputs
I won't claim that this is correct whatsoever, but briefly looking at your
set up, it is clear that the water isn't pulling extra load from the second
chiller. I think you may want to set up a single chiller because I don't
see a way to get the water to go through both chillers. You could also
create your own custom curves so that you match the combined performance of
the modeled chiller.
Just a thought.
Rob
On Fri, Apr 22, 2011 at 1:55 PM, Pasha Korber-Gonzalez
<pasha.pkconsulting at gmail.com> wrote:
Hi,
I could use some guidance to make sure I'm assuming the correct inputs to
set up chillers in series. This is the first time I'm trying to model this
and I have it set up with a primary & secondary loop for a total delta T of
16 across 2 chillers. I'm getting a run error of the secondary loop
having NO DESIGN FLOW/LOAD, but I'm not sure how to show that load on the
secondary loop.....maybe I have the chillers listed backwards???
Can anyone take a quick look at the setup in the Plant Module and let me
know what I am missing on this? I couldn't find any info on chillers in
series in the DOE-2 docs to guide me on the correct inputs and setup.
.pd2 & inp files attached.
Thanks in advance for your keen eye and guidance on my model.
Pasha
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20110422/338654fd/attachment-0001.htm>
More information about the Equest-users
mailing list